GE window a/c: compressor wont shut off.
#1
Member
Thread Starter
Join Date: Feb 2017
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
GE window a/c: compressor wont shut off.
When plugged in and the power button pushed the compressor comes on and wont shut off, even in fan mode. If I press the power button to turn off all the digital lights go out on the control board but "Only" the compressor is running.
I removed the control board thinking it might be the problem and when it was removed I plugged the a/c in and the unitl came on and a few seconds later the compressor came on. I could sure use some help.
Thanks in advance.
This is a GE 10,000 btu unit with control board 30562011 D2115A
I removed the control board thinking it might be the problem and when it was removed I plugged the a/c in and the unitl came on and a few seconds later the compressor came on. I could sure use some help.
Thanks in advance.
This is a GE 10,000 btu unit with control board 30562011 D2115A
#2
Welcome to the forums.
That is the display/control board. There is another board or some type of relay that controls the blower and the compressor. That's where the problem is. Most likely a stuck relay.
Without a model number I can't help much further.
That is the display/control board. There is another board or some type of relay that controls the blower and the compressor. That's where the problem is. Most likely a stuck relay.
Without a model number I can't help much further.
#4
In looking at that PS/switching board..... it looks like fairly old technology which means this must be a fairly old window A/C.
I've highlighted the relays. The two with the red arrows, I believe, are the fan relays and the one with the yellow arrow is the A/C compressor.
In re-reading your first post I'm not so sure it's a stuck relay as if it were.... the compressor would start as soon as the unit is plugged in. That leaves us with a logic problem that will be difficult to diagnose without test equipment.
I've highlighted the relays. The two with the red arrows, I believe, are the fan relays and the one with the yellow arrow is the A/C compressor.
In re-reading your first post I'm not so sure it's a stuck relay as if it were.... the compressor would start as soon as the unit is plugged in. That leaves us with a logic problem that will be difficult to diagnose without test equipment.