A/C coil air restriction.


  #1  
Old 02-27-17, 08:57 AM
S
Member
Thread Starter
Join Date: Feb 2017
Location: Us
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
A/C coil air restriction.

Forced air 2-stage Goodman furnace 5 yrs old. Heat flow under stage 2 is pleasantly robust. Example, Removing filter results in very robust heating air flow. Filter creates some air flow restriction. But I understand filter is needed.
If I have ac installed, will this create significant air flow slow down because of a-coil restricting air flow passage? Will it slow down airflow even more in similar fashion as the filter does?
 
  #2  
Old 02-27-17, 09:03 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
As long as the AC coil is clean it won't lower your air flow enough to cause a problem. What kind of filter are you using?
 
  #3  
Old 02-27-17, 05:27 PM
S
Member
Thread Starter
Join Date: Feb 2017
Location: Us
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Allergen pleated.
I like the Robust air flow w/out ac installed. I rarely use ac, but understand will need for resale when the time comes. Thought of getting it over with and installing, but don't want to slow down robust air flow during heating season.
Seems logical that air having to push through narrow fins of ac coil must slow airflow down a bit.
 
  #4  
Old 02-28-17, 05:00 AM
S
Member
Thread Starter
Join Date: Feb 2017
Location: Us
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
If anyone has any experience with or data on this, I'd appreciate hearing from you.
Thanks.
 
  #5  
Old 02-28-17, 06:12 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
I like the Robust air flow ...
In other words, you like the air roaring from the registers and blowing the drapes/curtains around. That puts you in a distinct minority as most people want a very gentle air flow that is imperceptible unless REALLY thinking about it. Such "robust" air flow is indicative of ductwork way too small.

To each their own.
 
  #6  
Old 02-28-17, 06:32 AM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 185 Upvotes on 169 Posts
A well designed duct system should handle airflow that shouldn't be noticeable when the equipment is running.
Also, those 1" pleated filters, especially the 3M brand, can severely restrict airflow. I recommend using the cheap 1" fiberglass throw away filters, the ones you can see through. If you require more filtration then move up to a 4" or 5" filter. Remember, the filter isn't there for you, it's there to keep debris out of the equipment.
Any coil will have a pressure drop. Static drop across a dry coil is actually one way to measure airflow. The manufacturer should have a table showing this in the manual and/or on the unit.
You'll want around 350-400 CFM per ton of cooling. The standard is ~400, lowering towards 350 for increased dehumidification.
 
  #7  
Old 03-07-17, 09:42 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
If thinking of installing A/C, U need to do a load-calc & Sizing...
The ductwork was probably sized for heating & might be too small when cooling is added.
HVAC Load Calculation - Maunualj - Whole House Loadcalc

Do everything U can to reduce the Btuh needed...
Make sure the duct system is properly sized with efficient airflow components...
 
 