Air Conditioning Not working; breaker shows red flag when on. I was an electrician ages ago but just wanted to know what the red flag is on the AC breaker.
The AC stopped working and this is what I saw in the panel; a photo is attached.
Any help is appreciated.


The AC stopped working and this is what I saw in the panel; a photo is attached.
Any help is appreciated.



#2
Member
Join Date: Nov 2007
Posts: 391
Received 0 Votes
on
0 Posts
A) It's tripped.
B) It's an illegal and dangerous install. That is a 240V circuit, and it MUST be a 2 pole common trip breaker that trips/disconnects both poles simultaneously. It was installed with two single pole breakers and an illegal handle tie. Circuit breakers are designed to trip even if the handle is wedged into the ON position. Normally when tripped, the handle will move to the center position (and Square D QO breakers will display the red trip flag). Because of the wire handle tie, when the one pole tripped out it did not generate enough force to flip the other handle to the off position. This means there is still a hot leg connected to the AC unit.
Pull those two breakers and replace them with a 2 pole QO breaker of whatever the original amp ratings are (probably 30A). Cost you about $20.
Now that doesn't mean there isn't still a problem with the AC unit that caused it to trip in the first place... But you need to resolve that issue first and see if it trips again..
B) It's an illegal and dangerous install. That is a 240V circuit, and it MUST be a 2 pole common trip breaker that trips/disconnects both poles simultaneously. It was installed with two single pole breakers and an illegal handle tie. Circuit breakers are designed to trip even if the handle is wedged into the ON position. Normally when tripped, the handle will move to the center position (and Square D QO breakers will display the red trip flag). Because of the wire handle tie, when the one pole tripped out it did not generate enough force to flip the other handle to the off position. This means there is still a hot leg connected to the AC unit.
Pull those two breakers and replace them with a 2 pole QO breaker of whatever the original amp ratings are (probably 30A). Cost you about $20.
Now that doesn't mean there isn't still a problem with the AC unit that caused it to trip in the first place... But you need to resolve that issue first and see if it trips again..
#5
Member
Join Date: Nov 2007
Posts: 391
Received 0 Votes
on
0 Posts
It was most likely a transient overload, maybe from the first startup of the year. However that doesn't change the fact that you HAVE TO change out the breaker for the correct one. It is dangerous as-is.