Trane XR11 compressor won't start


  #1  
Old 05-31-17, 11:25 AM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
Trane XR11 compressor won't start

I have a 12 year old Trane XR11 for cooling my home. Just a few days ago it stopped making cold air. Went out and checked it and the cold line isn't getting cold at all - nothing. Started taking it apart today and it seems like the compressor isn't turning on at all. Fan spins.

The start capacitor is a 97F9839 - 55 + 5 uf MFD 440 Volt VAC. I tested it with my fluke and got 52uf and 5uf. A little low on the compressor cap, but within range of the +/- 6% of it's labeled accuracy.

I also noticed the start relay buzzes, but stops when I press on it a little.

I didn't trust my listening for the compressor, so I disconnected the fan and left the compressor connected, then powered the unit back on. No noise at all, except the buzzing relay. I'm not sure if there is some failsafe to keep the compressor from turning on when the fan is off.

Ideas?
 
  #2  
Old 05-31-17, 11:37 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
No, the compressor should have ran. I always change the cap even if its a just little low. The contacts on the contactor must be worn if its buzzing.
 
  #3  
Old 05-31-17, 12:27 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
I went back and did some more testing. I decided to measure impedance across the 3 compressor motor lines. Kept getting OL when measuring from red-orange or red-black. So I removed the fan and followed the wires into the actual compressor. Sure enough, red wire was melted and burned off the connector.

Since the other wires don't seem harmed, I think I can rule out the compressor overheating. I suspect it was simply a loose connection that got really hot. So I'd like to crimp a new connector on but I'm not sure what those barrel type connectors are called, of if there is a better connector for that fat pin. Any ideas?

Oh, and I measured the compressor motor straight from the pins: 1.46 0.56, and 1.02 ohms.
Name:  IMG_4471.jpg
Views: 3904
Size:  42.0 KB
 
  #4  
Old 05-31-17, 12:48 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,168
Received 169 Upvotes on 137 Posts
You have flag type quick disconnect terminals, but you can use a straight version and it is easier to crimp properly:

https://www.lowes.com/pd/Utilitech-1...tors/999953182

The blue color is for 14 or 16 ga wire. Yellow is for 10 or 12 gauge. You will need a terminal crimp tool made for insulated terminals to crimp it properly.

You don't need to use an insulated terminal but they are often easier to find and it doesn't hurt to use one in place of a non-insulated.
 
  #5  
Old 05-31-17, 12:49 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
Look closely at the photo. It's a round pin maybe 0.1" diameter. It is not a flat quick connect.
 
  #6  
Old 05-31-17, 01:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Did the pin burn off from the compressor ? Looks like it in the picture.
If it did.... the compressor is gone.

Terminals like these work great for solid repairs.

Term-LOK-TLC310-Compressor-Terminal-Packard/dp/B004UW0GGC
Name:  repair.jpg
Views: 2601
Size:  5.8 KB
 
  #7  
Old 05-31-17, 01:13 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
I don't see any round pin? Your compressor numbers aren't looking to good, you might have lost the compressor.
 
  #8  
Old 05-31-17, 01:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Those resistances do look low but the spread is correct.

I do see the pin now. The terminal on the wire looks strange.

Name:  pin.jpg
Views: 3157
Size:  26.5 KB
 
  #9  
Old 05-31-17, 01:33 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
You can see the round pin more clearly by looking at the orange wire connection. They look like 1/4" quick connects but plug onto a round bullet type pin, not a flat blade.

I found a pretty close connector in my drawer of random stuff. I'm going to try to clean everything up and refit the wire.

Yes, the resistances seem low. I did also test to the compressor body and copper pipes and got OL, so it doesn't seem like I have grounded windings. My meter can't measure inductance, which would be useful.
 
  #10  
Old 05-31-17, 04:13 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was finally able to get my camera in for a better photo. It looks like the pins actually have 1/4" spades soldered or welded to them, then the quick connects slide over those. You can see the bit of something left on the side of the pin that lost it's wire.

I found a barrel connector that fit pretty tight over the pin and soldered it to the red wire, then sleeved it with a very thick rubber. I couldn't get my soldering iron into place to get the bit of spade off of the pin, but my connector seemed to fit really snugly so I just filed/sanded everything shiny and stuck it on.

Everything works great!

Probably should have used some connector paste or something. I can still go back and redo it pretty easily.

Oh, and yes, I cleaned all the leaves and crud out of the condensor
Name:  IMG_4473.jpg
Views: 3385
Size:  35.2 KBName:  IMG_4474.jpg
Views: 3332
Size:  51.6 KB
 
  #11  
Old 05-31-17, 06:48 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Those connectors I left you the link to work real good on round pins if you need something better in the future.

A was remiss in not mentioning to you to wear safety glasses or goggles anytime working on connections like that in case of a refrigerant leak
 
  #12  
Old 05-31-17, 07:58 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hmm, I wasn't being violent with anything so I don't think I was at too much risk. Not like that one time when I tried to drill a drip hole into the bottom of a window a/c frame...

I guess I wait and see if the wire melts again. It could have just come loose, or corroded and heated up from the resistance. Or there is something wrong with the compressor. Or both.

The compressor turns on and runs pretty smoothly so I'm hoping it's fine.
 
  #13  
Old 05-31-17, 08:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Anytime you mess with the wiring connections there is a risk.
 
  #14  
Old 05-31-17, 10:06 PM
C
Member
Thread Starter
Join Date: Jan 2012
Posts: 191
Upvotes: 0
Received 0 Upvotes on 0 Posts
Risk of a refrigerant leak when playing with electrical wires??

The power was off...
 
  #15  
Old 06-01-17, 03:54 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
The compressor is pressurized even with the power is off.
 
 