Condensor fan/compressor not running
Great forum. You guys have been great with my heating questions; hope you don't mind an AC one now that summer's almost here.
I installed a Hamilton central air unit 17 years ago and it has been flawless. I had it running yesterday for several hours, and all was fine. Then I noticed cool air ws no longer coming out of the vents. Checked outside, and the fan was not running; it seems the compressor ws not going either.
I checked all the connections today, and tried starting it up again. When I turn it on, the air handler fan runs fine. Outside, it just hums. If I spin the fan, it starts running but I think the compressor is still not running.
My guess is the capacitor? It's the original capacitor, has three leads - one to 240 volts, one to the compressor and one to the fan.
Does this make sense? Just replace it? Is there anyting else I should be considering?
Thanks.
I installed a Hamilton central air unit 17 years ago and it has been flawless. I had it running yesterday for several hours, and all was fine. Then I noticed cool air ws no longer coming out of the vents. Checked outside, and the fan was not running; it seems the compressor ws not going either.
I checked all the connections today, and tried starting it up again. When I turn it on, the air handler fan runs fine. Outside, it just hums. If I spin the fan, it starts running but I think the compressor is still not running.
My guess is the capacitor? It's the original capacitor, has three leads - one to 240 volts, one to the compressor and one to the fan.
Does this make sense? Just replace it? Is there anyting else I should be considering?
Thanks.
#2
Since the capacitor has 3 leads, it's a dual capacitor. One section is for the compressor, the other is for the fan. The fan running after giving it a "push" is a classic sign of a bad capacitor, so it's a safe bet that the fan side is bad. With any luck, the other (compressor) side is also bad, causing the compressor to not start. There's a good chance that replacing the capacitor will restore normal operation.
#4
It may be a little odd that both sides went bad at the same time, however it's not unheard of. For the price of a new capacitor, it's definitely worth trying.