Odd A/C & blower issues
#1
Member
Thread Starter
Join Date: Jun 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Odd A/C & blower issues
Hello! My apologies if duplicated, but I searched and didn't find any answers. Troubleshot my AC issues and replaced the dual capacitor. The AC started working again for a while. However, after a few hours, I noticed there wasn't any air coming out the vents. I went to the garage, and the blower was running (well, it was making noise, but no air flow). I powered everything down, started it up and still no go. Even if I turned the AC off and set the fan to run, no air coming out of the vents. I then powered everything down again, and turned on the heater. It started up and I could feel air coming out the vents. I turned everything off then turned the AC back on... and it started working. I'm sure this won't last. Ideas what could be causing this? Thanks in advance for any help!
#2
Group Moderator
Are you getting any blink codes on the control board?
I recently had an intermittent work, not work problem. It turned out to be a cracked solder joint on the control board for the relay that controlled the blower motor. The problem started out very intermittent but over time got worse and worse. Everything checked out OK so I looked at the control board. When it was running and I was poking around I happened to bump the relay and the fan quit working. After a close inspection it was a bad solder joint.
I recently had an intermittent work, not work problem. It turned out to be a cracked solder joint on the control board for the relay that controlled the blower motor. The problem started out very intermittent but over time got worse and worse. Everything checked out OK so I looked at the control board. When it was running and I was poking around I happened to bump the relay and the fan quit working. After a close inspection it was a bad solder joint.
#3
Welcome to the forums.
Yes.... that's because your evaporator coil was frozen over. Turning the heat on unthawed it.
You need to check for good air flow. Possible problems are clogged/dirty air filter.
If the air flow is ok.... you may be low on refrigerant.
I noticed there wasn't any air coming out the vents. I went to the garage, and the blower was running
You need to check for good air flow. Possible problems are clogged/dirty air filter.
If the air flow is ok.... you may be low on refrigerant.
#4
Member
Thread Starter
Join Date: Jun 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks everyone for the replies! Sorry for the delay. I couldn't recall the name of the site, and it took some time to find where I posted this question. lol (Been a crazy week! Uncle passed away, 95-100 temps outside and my house getting into the mid 80's downstairs, low 90's upstairs everyday!)
When I try turning the heat on, and the blower won't start, I get 4 flashes ="Open high temperature limit switch". Could be due to having to set the temperature in the mid-80's just to get it the heat to turn on? (Since my house is in the mid 80's by late afternoon)
I'm not getting any blink code when the AC is running, the blower sounds like it is running, but low to zero air flow.
If I run the heat for awhile, or leave it off for a few hours, it doesn't always fix the air flow. Perhaps I need to clean the evaporator coils? I found this article: https://www.handymanhowto.com/how-to...-coils-part-1/ but my system doesn't look like that. (not exactly) I'm going to take apart the top part and hope that's where the coils are.
Again, thanks!!
Are you getting any blink codes on the control board?
I'm not getting any blink code when the AC is running, the blower sounds like it is running, but low to zero air flow.
Yes.... that's because your evaporator coil was frozen over. Turning the heat on unthawed it.
Again, thanks!!
#5
Sorry for your loss. 
The board won't cause any A/C problems and doesn't really control the A/C other than the blower.
It sounds like you have a low airflow issue. Yes the coil could be dirty.
Has the filter been changed ?

The board won't cause any A/C problems and doesn't really control the A/C other than the blower.
It sounds like you have a low airflow issue. Yes the coil could be dirty.
Has the filter been changed ?
#6
Member
Thread Starter
Join Date: Jun 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It sounds like you have a low airflow issue. Yes the coil could be dirty. Has the filter been changed ?

Once I turned on the AC back on, I could feel a big difference in the airflow, but only a little cool. Sounds like I need to pay an HVAC guy to recharge it.

Thoughts/suggestions? Again, THANKS!
#7
Member
Thread Starter
Join Date: Jun 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
New Problem as of July 24
Hello! My AC issues continue! So much fun! 
I replaced the dual capacitor, and the AC unit outside started turning on, and has been running. However, now I have a new issue. I turn on the AC, and the fan on the outside unit turns on, but then after a few seconds I get an odd sound, the fan starts, then starts back up again. Here is a link to a video:
https://youtu.be/_T_0lZDbjdo Does it seem like maybe one half of the new dual capacitor has once again failed?
Thanks in advance for any and all help!

I replaced the dual capacitor, and the AC unit outside started turning on, and has been running. However, now I have a new issue. I turn on the AC, and the fan on the outside unit turns on, but then after a few seconds I get an odd sound, the fan starts, then starts back up again. Here is a link to a video:
https://youtu.be/_T_0lZDbjdo Does it seem like maybe one half of the new dual capacitor has once again failed?
Thanks in advance for any and all help!

#8
That momentary interruption of power to the contactor is most likely caused by a low refrigeration problem. That cannot be allowed to continue like that or you will risk losing the compressor.
My recommendation is to have the refrigerant level checked as soon as possible.
My recommendation is to have the refrigerant level checked as soon as possible.
#9
Member
Thread Starter
Join Date: Jun 2017
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
PJmax -That momentary interruption of power to the contactor is most likely caused by a low refrigeration problem. That cannot be allowed to continue like that or you will risk losing the compressor.
My recommendation is to have the refrigerant level checked as soon as possible.
My recommendation is to have the refrigerant level checked as soon as possible.
Crud. I was hoping for a fix I could do without paying someone, due to "cash flow issues".
I did a little more inspecting and noticed that one of the neutral wires was arcing against one of the power wires. Not sure why the insulation was worn thru... I cut out the bad wires, replaced a connector, heat-shrinked both wires, and reconnected it. Seems to start up fine now... Fingers crossed.