A/C unit won't start up until reset every time


  #1  
Old 07-17-17, 06:44 AM
G
Member
Thread Starter
Join Date: Jul 2017
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
A/C unit won't start up until reset every time

Hello, I have a Bryant all in one outside unit. A couple days ago an issue started I can't pinpoint the cause of. The unit functions normally when running, however, when it reaches desired temperature and kicks off, it will not start back up until I reset the breaker, turn the thermostat to the off position and wait a few minutes and then flip back to cool. Sometimes it only takes this process to be done once and someone I have to perform this process repeatedly to get the unit to start back up. I am an automotive technician and I am not very familiar with home HVAC. I understand the basics but am not very familiar with home thermostats and the electrical and safety switch portions of home HVAC. Any help would be highly appreciated as my wallet is a little light at the moment. Thank you
 
  #2  
Old 07-17-17, 07:20 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Is it tripping the breaker?
 
  #3  
Old 07-17-17, 09:37 AM
G
Member
Thread Starter
Join Date: Jul 2017
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
No, the breaker is not tripping, it is not even getting warm. The only way the unit will restart is if I turn the breaker off and back on and then go inside and turn the thermostat to off, wait a few minutes and then turn it back to the cool position. Sometimes I will have to repeat this process several times to get the unit to turn on
 
  #4  
Old 07-17-17, 10:13 AM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,402
Upvotes: 0
Received 5 Upvotes on 5 Posts
Make sure the breaker is good, then I'll check the thermostat. you can remove the T-stat cover, jump R,G,Y wires to see if that start the system.
 
  #5  
Old 07-17-17, 10:16 AM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,554
Received 59 Upvotes on 50 Posts
If your compressor/condenser (outside unit) has a Time Delay Relay (TDR), it could be your problem. It's purpose is to prevent the compressor from turning on too soon after it turned off, however if you have a digital thermostat, there is a 5 minute delay built into the thermostat (thermostat won't call for cooling until at least 5 minutes after it last called for cooling). You probably have circuit diagram inside the cover of the outside unit. If your unit has a TDR (not all units do), you can either check with a voltmeter the next time the A/C doesn't come on, or just try jumpering around it. FWIW, I had this problem with my 5 year old Bryant system. It's now ~25 years old and still running fine with the TDR jumpered out.
 
  #6  
Old 07-17-17, 11:50 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
When you say breaker are you taking about the disconnect outside?
 
  #7  
Old 07-17-17, 03:57 PM
G
Member
Thread Starter
Join Date: Jul 2017
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you. I took the thermostat of the wall and hooked the red, green and yellow wired together and it started fine every time I tried all the wires. This told me it was the thermostat that was the problem (I beleive). Put a cheap thermostat in and out send to be staying every time now. Thank you for your replies an info on the TDR as it may save me in the future.
 
 