Zoned HVAC system, intermittent damper issue

I am experiencing the following issue with my system.

I have a Carrier HVAC system that supplies the second and third floor of my home. The system is approximately 4 years old. It worked without issue for the first three years of service.

The system is controlled with a Honeywell Zone control board model HZ311 and uses Honeywell 7 day programmable thermostats.

The system exhibits the following behavior. On occasion, approximately once a week the third floor does not receive airflow when the thermostat is calling. It usually occurs later in the day or early evening after the system has cycled 7 15 times. Best I can tell is that the damper does not open. I have worked with a local HVAC company who has visited my home six times without solving the problem.

To date they have replaced the zone control board twice and switched the thermostats between the second and third floor. Neither of these has eliminated the problem. They have also indicated that the damper is not obstructed.
 
Sponsored Links
  #2  
Old 07-18-17, 09:23 AM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
Hmmm, six times? Does the problem occur when he is there? Is there anything you do to get it working again?
 
  #3  
Old 07-18-17, 05:13 PM
Member
Join Date: Jul 2017
Location: US
Posts: 3
Received 0 Votes on 0 Posts
To repeat what skaggsje said, does the problem occur while they're there? Considering they replaced the controller twice and replaced both thermostats, I'd be interested in reading what they found the last 6 times they were there.

I'm not too familiar with this specific zone controller since I primarily do commercial work but one thing I'd look at when the issue does pop up is verify the thermostat is calling for cooling. Then go to the controller and verify the 24v (?) signal is being input there from the thermostat. Then verify a signal is being output to the damper actuator from the controller. Then finally going to the actuator and making sure it's getting the signal and responding accordingly. You could just go to the actuator to begin with as well.

If it worked fine the last 3 years, chances are something might be intermittently failing assuming the setup and all the settings have remained the same. If you have new thermostats and a new controller, the wiring and/or actuators might be having problems.

If you don't have it already, here is an installation guide on that controller. Might be good during some toilet time:

https://forwardthinking.honeywell.co...69_2069efs.pdf
 
  #4  
Old 07-18-17, 07:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,689
Received 343 Votes on 321 Posts
You didn't mention how the three zone LED's were responding.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: