Carrier Infintity System Fault Code 198, Input G Alert

My Carrier Infinity FE4ANB006 heat pump is terrific for cooling and dehumidifying my Florida home but for the past week, INPUT G ALERT and FAULT CODE 198 are displayed on the control panel. I've contacted the installer, but haven't heard back from them. .

Perhaps this is important: the electrical power was out for one week in my area from Hurricane Irma. These fault codes appeared after the power came back on.

An Internet search did not reveal anything for code 198 or Input G alert.

My system is cooling/dehumidifying satisfactorily.

What do these codes mean? How to address them?
 
Sponsored Links
  #2  
Old 09-24-17, 12:49 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
Input G usually means a drain issue.

What thermostat do you have ?
Infinity color touch screen or monochrome Infinity with buttons?

The Infinity thermostats may be able to define code 198.
 
  #3  
Old 09-24-17, 12:50 PM
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Thanks for the reply.

My system is the color Infinity touch screen.
 
  #4  
Old 09-24-17, 01:00 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
Have you tried getting the thermostat to define the problem?

Surf to the service picture of a hat, push and hold it for about 12 seconds and it will turn a yellow green.
Surf to service and then select last 10 system events.
 

Last edited by Houston204; 09-24-17 at 01:45 PM.
  #5  
Old 09-28-17, 05:04 PM
Member
Thread Starter
Join Date: Sep 2017
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
SOLVED.

The Safe-T-Switch float switch (next to the indoor air handler) reservoir had enough water in it to elevate the floating sensor.

I pulled the float switch out of PVC tube holder, dumped out the water, then replaced the Safe-T-Switch.

The error message FAULT CODE 198, INPUT G ALERT message is now gone.

Houston204: I did what you said, holding the "hat" icon and found the system events. That was very interesting. Thank you.

All is normal now. Thank you.
Dag
 
  #6  
Old 09-28-17, 06:06 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
You will need to blow out the drain to prevent another float switch trip.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: