Fujita KFR-53GW/m a/c

My a/c was out of commission for approximately 3 years. I inspected it, cleaned it and had it re-gassed. It switched on normally and operated as expected for 5 to 8 minutes when both the outside fan and compressor stopped. The inside air temperature was 30 deg C and the selected temperature 23 deg C. After a while the outside fan and compressor came on again. This is the cycle it is running continuously. The result is that the selected temperature is not reached.
I suspected an overheat in the compressor causing it to switch off. I measured the volts on the terminal board in the outside unit and it indicated that the power is off for both the fan and the compressor if stopped.
The a/c is a 18000 BTU system with 3 sensors. One in the outside unit, one on a pipe in the inside unit and one for the incoming air.
Any ideas an/or suggestions will be appreciated.
Julian


mod note: member from S. Africa
 

Last edited by PJmax; 09-26-17 at 09:25 AM.
Sponsored Links
  #2  
Old 09-26-17, 08:05 AM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Sounds like it shutting down on low pressure safety.
 
  #3  
Old 09-26-17, 09:17 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,954
Likes Received: 154
Welcome to the forums.

You should put non-US in your personal bio.

This is a ductless multiple evaporator split heat pump system.
These systems are not cut and dry to repair. There is a control board that monitors all the operating parameters. Any one is incorrect shuts the system down.

There should be a diagnostic control board....possibly with indicators.

I've been trying to find on-line service info and have not found anything usable. You need the service manual to even start to diagnose the unit.
 

Last edited by PJmax; 09-26-17 at 09:48 AM.
  #4  
Old 09-27-17, 10:30 PM
Member
Thread Starter
Join Date: Sep 2017
Location: South Africa
Posts: 3
Pete, Thank you for your interest. I will pursue your suggestion to find a service manual.
Julian
 
  #5  
Old 09-27-17, 10:37 PM
Member
Thread Starter
Join Date: Sep 2017
Location: South Africa
Posts: 3
skaggsje, Thank you for your response. I will ask the person that re-gassed my a/c and discuss your thought about the problem I experience.
Julian
 