Heat pump issues

Bought a new Goodman GSZ130361 Heat Pump had it installed and it runs for about a minute and shuts off (opens contactor). It was a scratch and dent unit (looks like light sheet metal damage thats it). For the time it runs compressor pulls 40 amps for a second and than settles down to 8 amps. Pressures are looking good. So bypassed the high and low limit switch no change. Replaced the board with new one , no change. Replaced the contactor with a new one, no change. I can get it to run if I put the thermostat wire directly to the contactor and bypass the board. It runs great cools and heats and sounds fine. Its currently working with that.

I'd like to set it up right. What am I missing? This unit is NEW.
Help.
 
  #2  
Old 10-28-17, 02:56 AM
M
Forum Topic Moderator
Join Date: Mar 2005
Location: USA - N.E.Tn
Posts: 45,166
Received 742 Upvotes on 648 Posts
Welcome to the forums! ..
Why not get the installer to come back and fix it? both the installation and parts should be under warranty.
 
  #3  
Old 10-28-17, 04:29 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
According to the model number that's not a heat pump, it's straight AC.
 
  #4  
Old 10-28-17, 11:17 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
If you’d like to get it set up properly, let’s start by filling this out. Correct commissioning of the unit is essential to proper operation.

http://hvac-talk.com/vbb/attachment....1&d=1489971253

Regarding your issue, use a meter to determine where your loosing control voltage. Don’t jump things out, that’s not troubleshooting. It’s guessing.
 
  #5  
Old 10-28-17, 11:33 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
That is a 3 ton 13 SEER heat pump condensor.
Not sure how the commissioning form is going to help here. It certainly can't be posted here.

It sounds like the member bought his own heat pump condensor and had it installed. That makes him liable for repairs or pay the installer to troubleshoot it. Fair is fair.

It sounds to me like you have the wiring from the air handler to the condensor incorrect. There should be at least five wires connecting the two.
R - red 24vac.
C - black/blue - common.
O - orange -reversing valve.
W - white - electric heat activation.
Y - yellow - compressor.
 
  #6  
Old 10-28-17, 11:57 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
It will give the OP an idea of what’s involved getting the unit setup correctly, at least as far as topics not related to charging.
This member was on another website. He said he bought a scratch and dent unit and had a friend install it, but the friend has not been able to figure out what’s wrong with it.
 
  #7  
Old 10-28-17, 12:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Gotcha.

The problem pretty much centers around the defrost board. If power is being supplied from the house and applying it directly to the contactor keeps it running.... it's not getting thru the defrost board. The d' board is not connected properly or is defective.
 
  #8  
Old 10-30-17, 03:07 PM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
Any update OP? Have you fixed your issue?
 
 