HVAC Blower will not shut off

Reply

  #1  
Old 05-09-18, 07:53 AM
Member
Thread Starter
Join Date: May 2018
Location: USA
Posts: 1
Received 0 Votes on 0 Posts
HVAC Blower will not shut off

Hi I have a trane unit TWE060b150b0 and the blower runs constantly i have had two havoc techs out with no solution. contactors have been changed and even unplugging the controls board the fan still runs i have even completely unhooked the thermostat and its till running. its also calling for heat when the thremostat is connected any help would be greatly appreciated
 
Sponsored Links
  #2  
Old 05-09-18, 02:36 PM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
Are you saying that you have the stat heat?
 
  #3  
Old 05-09-18, 04:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,668
Received 340 Votes on 318 Posts
Welcome to the forums.

That model number is close to a heat pump air handler. If you have electric reheat coils in that air handler then a likely problem is a defective sequencer. A sequencer is a timer and relay in one. It controls the blower when in heat mode. They get stuck with the blower section on.

I'm trying to locate a service manual. That unit may use a timer module for the blower.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off