HVAC Blower will not shut off


  #1  
Old 05-09-18, 08:53 AM
U
Member
Thread Starter
Join Date: May 2018
Location: USA
Posts: 1
Likes: 0
Received 0 Likes on 0 Posts
HVAC Blower will not shut off

Hi I have a trane unit TWE060b150b0 and the blower runs constantly i have had two havoc techs out with no solution. contactors have been changed and even unplugging the controls board the fan still runs i have even completely unhooked the thermostat and its till running. its also calling for heat when the thremostat is connected any help would be greatly appreciated
 
  #2  
Old 05-09-18, 03:36 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Likes on 0 Posts
Are you saying that you have the stat heat?
 
  #3  
Old 05-09-18, 05:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 70,979
Received 3,174 Likes on 2,850 Posts
Welcome to the forums.

That model number is close to a heat pump air handler. If you have electric reheat coils in that air handler then a likely problem is a defective sequencer. A sequencer is a timer and relay in one. It controls the blower when in heat mode. They get stuck with the blower section on.

I'm trying to locate a service manual. That unit may use a timer module for the blower.
 
 