A/C Condenser fan stiff only when power is on

My condenser fan isn't running, compressor runs ok, but switched off since I don't want to potentially burn out the compressor.

When the power is on, the fan blades are difficult to turn and won't go more than a quarter turn when I push it with a stick.

With the power off, the fan turns effortlessly.

Is it time for a new fan motor, or should I try to replace the capacitor first?
 
  #2  
Old 05-30-18, 05:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,935
Received 3,950 Upvotes on 3,543 Posts
Welcome to the forums.

I always recommend testing or replacing the capacitor first.
 
  #3  
Old 05-30-18, 07:00 PM
C
Member
Thread Starter
Join Date: May 2018
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks! I will get one tomorrow and try it.

Unfortunately my multimeter is deep in hiding, else I would have tested it already.
 
  #4  
Old 05-31-18, 07:39 AM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,500
Received 68 Upvotes on 62 Posts
It is likely that the fan motor bearings are worn out.
With worn bearings when power is applied the rotor pulls sideways and jams either the rotor against the stator or the shaft against the bearing.

You could try to move the motor shaft from side to side and try to detect any movement.
 
  #5  
Old 05-31-18, 11:49 AM
C
Member
Thread Starter
Join Date: May 2018
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yup, definitely the motor. Now on to find a replacement for a 20 year old part.
 
 