AC buzzing, won't engage

So I already tried to troubleshoot what already appears to be a common issue in the when the unit buzzes and the fan motor won't spin, it is either a bad capacitor, bad motor, or both. I have already replaced both the motor and capacitor and am still getting the buzzing without the motor engaging. One video I watched, the gentleman said that the motor needs a minimum of 70+7 uf capacitor, however, the one that I pulled out of the unit was 40+5uf. I tried to look up specs/requirements of the new motor (which was the same as the one I replaced) and could not find anything that suggested how much uf it needed. So I guess this would be a two part question; is a 40+5 capacitor enough or should I return for a 70+7? And if that is enough, what is the next step in diagnosing why the fan motor wont spin?

Thank you in advance.
 
Sponsored Links
  #2  
Old 06-13-18, 12:46 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,471
Received 11 Votes on 8 Posts
You have a dual capacitor. The larger value of the two (40) is used by the compressor, while the smaller (5) is the fan capacitor. The fan capacitor should be the value specified for the particular motor. Bigger is not necessarily better.

It's unusual for a new motor and capacitor to not startup. The replacement motor should have come with something stating what the proper capacitor value is. Does the fan motor spin easily?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: