Contactor Sticks and can't find exact replacement


  #1  
Old 06-23-18, 12:23 PM
A
Member
Thread Starter
Join Date: Jun 2018
Location: usa
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Contactor Sticks and can't find exact replacement

Hi All,

I am struggling to find a direct contactor replacement that is on a Trane 1984 Central Air Unit. I have serial number and model BTD724A100X0
Anytime I order one online they come back way different. I have a few with highlighted examples of new vs old contactor. Any ideas....

SPECS for contactor on the unit right now.
Pole 1
LRA 18
FLA8
Pole 2
LRA 90
FLA 18

The item I was recommended and purchased Model 5MMA7
240V and all its says is
LR125
AMP
FL30
277volts

Process**** I have put in the new contactor and it fails to turn the unit on outside. I matched up each of the wires and then traced the thermost wires to the ac and noticed there is a sodder stem on the terminals.

I matched up the location on each side and nothing. When I manually push the contactor down everything works compressor etc. I have switched up the themro wire combination and nothing works. I thought maybe i shorted things out but I replaced the new contact with the old one that was on there and everthing works like a charm..it just sticks every so often because its old. Any ideas? Please see pics the ONLY thing different from the old vs new is one of the upper terminals has a post where are the new one has a flat metal screw hole. I belive amps and switch is same.

Any ideas would be greatly appreciated...
 
Attached Images       
  #2  
Old 06-23-18, 03:51 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,637
Received 77 Upvotes on 68 Posts
It appears that the 5MMA7 contactor has a 240V coil. Most US A/C systems use a 24V coil. When your thermostat calls for cooling, it sends 24VAC to the contactor coil. This causes the contactor contacts to pull down, turning on the outside unit. However, since the contactor you purchased has a 240V coil, it requires 240V rather than 24V to make it turn on. That's why it's not working. Purchase a contactor with a 24V coil and it will likely work fine.
 
  #3  
Old 06-23-18, 04:26 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
The equivalent 24v would be 5MMA5

Most would just use a generic 24v 30a contactor but generic has different connects that you have to deal with.
 
  #4  
Old 06-28-18, 05:04 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
Hi, can you post a pic of the wiring schematic, it’s a bit hard to see the connections on the contractor ,as mentioned a standard 30 Amp 2 pole contractor with a 24 VAC coil would work.
Geo
 
 