Want to add a fan wire to a two wire system

I have a Coleman/mix Honeywell furnace. Runs on two wires. Iím looking to add a fan wire to be operate off of nest.
The furnace has fan / limit control system Honeywell L4064B,
Heat system transformer, and the main two wires hook to a 3 way where two wire goes the HST then to the L4064B. Is there way I can add a g (fan) wire from nest. If so, where do I hook up to in the furnace?
 

Last edited by J2018; 07-06-18 at 06:31 PM. Reason: Errors
  #2  
Old 07-06-18, 09:30 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
No simple solution without adding parts. Most of those furnaces with a fan/limit switch need to have a relay added to support fan control. A few offered an official a/c conversion kit that included a relay for fan control.
 
 