Installed new contactor now compressor runs all the time.

Reply

  #1  
Old 07-14-18, 12:21 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Installed new contactor now compressor runs all the time.

My contactor in my Trane XE1000 had been sticking occasionally and the compressor would not shut off. So I ordered a new one and installed it but now the compressor runs all the time. As soon as I flip the outside breaker on the compressor starts running without the fan and stays running.
The old contactor is a Siemens 45GG20AJ
The new contactor is CTR02574
I'm attaching photos of the old and new contactors. I put the wires in the exact same positions but that isn't working. What wires do I need to switch?
 
Attached Images   
Sponsored Links
  #2  
Old 07-14-18, 12:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,674
Likes Received: 115
Do you have any pictures from further away... wider view ?
I'm looking for the lines coming in from the house and don't see them.
 
  #3  
Old 07-14-18, 12:32 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Ok, found a picture that shows the entire wiring area.
 
Attached Images  
  #4  
Old 07-14-18, 01:45 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Now that the rain stopped, here's some wiring pictures.
 
Attached Images   
  #5  
Old 07-14-18, 01:56 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,339
Likes Received: 3
It looks like you replaced a 2 pole contactor with a single pole contactor.

You might try reversing the single leg that is getting broken.

You are breaking the black leg ( Common) but need to break the red leg ( Run)

 
  #6  
Old 07-14-18, 02:01 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
So would that be switching L1 and L2? Or T1 and T2?
 
  #7  
Old 07-14-18, 02:03 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,339
Likes Received: 3
Unwire the contactor completely and spin it 180 degrees.
 
  #8  
Old 07-14-18, 02:08 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Could I also just swap sides for the wires? That way the L and T markings would remain on the correct ends.
 
  #9  
Old 07-14-18, 02:10 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,339
Likes Received: 3
Yep, you can swap L1 and L2 and then swap T1 and T2.

Be sure to also get those back wires on L1 and L2 or you are going to get a big spark.

I don't see that L1 and L2 is labeled on the new contactor but it might be on the other side.
 
  #10  
Old 07-14-18, 02:12 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Got it. I'll swap L1 and L2 and also T1 and T2 and all their associated push connectors.
 
  #11  
Old 07-14-18, 02:18 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,339
Likes Received: 3
I would also try to secure that run cap.
That unsecured capacitor can fall over and become a hazardous condition.
I always use a small piece of plumbers strap and a couple of 1/2" long screws.

I have seen capacitors fall over and burn a hole in the panel.
I have also been electrocuted by them.
 
  #12  
Old 07-14-18, 03:01 PM
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Ok, I switched all the wires and turned the breakers back on and waited the 5 minutes for the thermostat to kick in and it started up correctly. It's running now and will be for a while since the house got hot while I was doing all this.
Good idea on the plumber's strap. I'll get that and a couple sheet metal screws.
Thanks for the help.
 