AC not blowing through vents

We are getting no air through the vents at home. The outside unit is making noise and the fan is working. We replaced the capacitor and the motor but still no luck. Something isnít allowing the motor to run. Iím at a loss. The HVAC guy is coming tomorrow but I figured if anyone had any ideas before then it might help. Thanks!
 

Last edited by Wiegman; 07-30-18 at 02:58 PM.
Sponsored Links
  #2  
Old 07-30-18, 04:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,672
Received 340 Votes on 318 Posts
Welcome to the forums.

You replaced the capacitor and blower motor. Did you check for 120vAC to the motor ?
Is this a split A/C system only or an A/C system on a furnace ?
 
  #3  
Old 08-06-18, 06:20 AM
Member
Thread Starter
Join Date: Jul 2018
Posts: 2
Received 0 Votes on 0 Posts
Itís an AC on the furnace. Iím not sure about the first part of the question but the HVAC guy came out and said it was the circuit board. He told us it would be about $2000 installed to replace!! 😮 Luckily we got a few other more reasonable quotes around $525-$700.

Ultimately we we found out one of our friends had done it before. We ordered a new board and replaced it ourselves. Thanks for your help!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: