Defrost termination / fan delay switch

I have a box thatís 64f. How long should it take for the fans to cut in. This switch is a 35f switch, but itís attached to the end housing not the U bend. Itís a Trenton walk-in freezer.
 
Sponsored Links
  #2  
Old 08-06-18, 10:57 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,658
Likes Received: 113
That would depend on the model of the switch.
It should activate at 35 allowing the coil to start chilling before the fan restarts.
 
  #3  
Old 08-06-18, 04:19 PM
Member
Thread Starter
Join Date: Nov 2002
Location: Massachusetts
Posts: 1,815
I waited almost 30 minutes and it was all frosted =32f so I called it junk, ordered another, tested it in icewater before installing, and I was surprised it took about 8-10 minutes. Today, I put it in, returned from coffee and the box was 32 and the fans were running. Im thinking, under normal circumstances, the coldness of the walk-in freezer will speed up that time VS doing this from a hot pull down of 75F.
 
  #4  
Old 08-06-18, 04:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,658
Likes Received: 113
Yes...the cold box will speed the process up.
 