Upgrading Thermostat
#1
Member
Thread Starter
Join Date: Aug 2018
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Upgrading Thermostat
Good evening,
Would like to see if anyone is able to confirm I installed my new RTH8580ZW unit. My old unit was a RTH6350.
I was able to open my air handler and verify the wires leading to the thermostat. Two things I noticed, the Y1 and Y2 are bridged at the air handler for the old unit. Should that remain?
The old unit did not have a C wire (it was taped off) so I got that ready and connected it to the new unit along with all the other wires. After 1hr of checking, I powered up the unit and only received hot air. After another 40 minutes of checking all the setting on the new unit, setting system menu 0170 to #7 and 0190 to #0, the unit still would only produce hot air. I pulled out my meter and found the R to O was zero, checked the connection and now have cold air.
Inside the handler I have a flashing C2 code. High stage cool - Legacy mode only. Is this correct?
I have attached three images, one from the old thermostat, one from the new and the wire block on the handler. Could someone take a look and see if I have everything correct? Thanks a bunch up front.
Old unit

New Unit

Handler

thanks again for your help and support.
Would like to see if anyone is able to confirm I installed my new RTH8580ZW unit. My old unit was a RTH6350.
I was able to open my air handler and verify the wires leading to the thermostat. Two things I noticed, the Y1 and Y2 are bridged at the air handler for the old unit. Should that remain?
The old unit did not have a C wire (it was taped off) so I got that ready and connected it to the new unit along with all the other wires. After 1hr of checking, I powered up the unit and only received hot air. After another 40 minutes of checking all the setting on the new unit, setting system menu 0170 to #7 and 0190 to #0, the unit still would only produce hot air. I pulled out my meter and found the R to O was zero, checked the connection and now have cold air.
Inside the handler I have a flashing C2 code. High stage cool - Legacy mode only. Is this correct?
I have attached three images, one from the old thermostat, one from the new and the wire block on the handler. Could someone take a look and see if I have everything correct? Thanks a bunch up front.
Old unit

New Unit

Handler

thanks again for your help and support.
Last edited by PJmax; 08-30-18 at 04:44 PM. Reason: added pics from link/labeled one pic
#2
Advanced settings.....
170 -- 7
180 -- 1
190 -- 0
Your wiring is correct.
An extra wire inside the stat cable would be needed to run the condenser in two stage mode.
170 -- 7
180 -- 1
190 -- 0
Your wiring is correct.
An extra wire inside the stat cable would be needed to run the condenser in two stage mode.
#3
Member
Thread Starter
Join Date: Aug 2018
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Good morning,
Thanks for the quick reply. There is a spare wire in stat run. This would bring up two questions, the benefit and where the connections would go.
Thanks again for your help and support.
-David
Thanks for the quick reply. There is a spare wire in stat run. This would bring up two questions, the benefit and where the connections would go.
Thanks again for your help and support.
-David
#4
Your new wire would go to......
Y2 on the stat.
Y2 on the control board after removing the Y1 - Y2 jumper.
Y2 outside at the condenser board.
I'm not sure if there is something that needs to be changed out at the condenser. If there is a Y1-Y2 jumper..... it gets removed. If not..... there may be a dip switch setting on the board.
Y2 on the stat.
Y2 on the control board after removing the Y1 - Y2 jumper.
Y2 outside at the condenser board.
I'm not sure if there is something that needs to be changed out at the condenser. If there is a Y1-Y2 jumper..... it gets removed. If not..... there may be a dip switch setting on the board.
#5
Have we determined that the heat pump is two stage?
What is the model number of the outdoor unit?
What is the model number of the outdoor unit?
#6
Member
Thread Starter
Join Date: Aug 2018
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Good evening,
Sorry it too so long to respond, I found my notices going into my spam filter.
I have a Goodman (Amana) ASZ140361BB outside. I have no idea if it is a two stage unit. Thanks for your help ad advice.
Sorry it too so long to respond, I found my notices going into my spam filter.
I have a Goodman (Amana) ASZ140361BB outside. I have no idea if it is a two stage unit. Thanks for your help ad advice.