are they compatible?
i have a Rheem model #14aja42a01 condenser with matching coils. I also have a Rheem model #reab 1415j furnace. I was wondering if they are compatible? I know the condenser is 3.5 Ton and furnace is 3 ton I just don’t know if that would cause a problem.
#2
Member
reab1415j appears to be rated for 1400 cfm which translates to 3 1/2 ton (standard 400 cfm/ton) so no issue.