Line to PTAC Unit

Good Morning,

Retired Building Contractor with minimal electrical knowledge with a question!

I'm installing a 9000 btu Amana Air/Heat Pump (through-wall) unit and need some confirmation or advice on the Breaker, Wire, and Receptacle.

The PTAC unit is rated for 230/208 volts, volt range 197 to 253, Max Overcurrent Device is rated at 15 amps. It has a permanent cord rated at 15amps 240Vac.

What I have already installed: 15amp breaker in the panel box, 10/2 wire running to the unit, and purchased a Hubbell single receptacle rated at 20amps 250v w/ horizontal blades and ground.

What I need to know is, do I use the white wire also as a hot, since the receptacle has two brass screws? If so, in the panel box can I attach the white wire to the other side of the screw opposite the black wire on the 15amp breaker, or should I replace it with a 2 pole 15amp breaker?

Or, does anyone suggest another option?
 
Sponsored Links
  #2  
Old 11-09-18, 08:45 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,659
stop stop stop! Please use a double pole breaker!!!!
 
  #3  
Old 11-09-18, 10:18 AM
Member
Thread Starter
Join Date: Jun 2015
Location: US
Posts: 10
Okay, no problem I can do that. Do you see any other problems with my questions, or do you have any other suggestions? In other words am I good to go after switching out the single pole breaker for a double pole breaker?
 
  #4  
Old 11-09-18, 10:20 AM
Member
Join Date: Oct 2016
Posts: 775
I’m not quite sure what your attempting but your getting ready to cause an electrical fire.
You have a 208-230V unit. You need a double pole breaker.
 
  #5  
Old 11-09-18, 12:48 PM
Member
Thread Starter
Join Date: Jun 2015
Location: US
Posts: 10
Okay, so I switch out the single pole 15 amp breaker to a double pole 15 amp breaker, and everything else I described is good to go?
 
  #6  
Old 11-09-18, 01:39 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,659
Same two wires going to the breaker must go to each hot side of the receptacle
 
  #7  
Old 11-09-18, 02:26 PM
Member
Thread Starter
Join Date: Jun 2015
Location: US
Posts: 10
Okay Great, that helps thanks!
 