Hello!
I'm installing four small fridges in my farm stand (QBD model DC7HG, or Pepsi fridges). The FLA for each one is only 3.0A, but the LRA is a whopping 21.3A. I had planned use two 15A circuits and put two fridges on each one. I'm guessing this is large enough, even when pulling the LRA for a split-second, since none of these fridges have a 20A plug. But I'd like to make sure. Any comments?
Thanks.
 
  #2  
Old 05-21-19, 08:45 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 24,703
Received 785 Votes on 722 Posts
I don't know if they would even pull their locked rotor amperage when starting. I would say you are safe but if you want extra margin you could install two 20 amp circuits to give you a little more room.
 
  #3  
Old 05-21-19, 10:40 AM
airmark's Avatar
Member
Join Date: Feb 2019
Location: usa
Posts: 55
Received 4 Votes on 3 Posts
Due to the actual voltage drop during startup, the device will draw about 70% of the LRA. So a 15 amp circuit will probably work for a single refrigerator without tripping the breaker during startup. But if you put two refrigerators on a circuit then you can expect the circuit breaker to trip everytime after a power outage and subsequent startup. The combined LRA will be closer to 30 amps during simultaneous startups. Therefore you should only put one refrigerator on each 15 amp circuit.
 
 