Constant ac problems


  #1  
Old 08-07-19, 07:55 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Constant ac problems

Hey everyone,

looking for for a little help. I have a trane gam5a0b30m21sab that was built in 2013, and have had constant problems the last year. The most recent issue I have is that the coils are freezing, I had a company check refrigerant level and it wasnít only about a pound low, Iíve checked to see if the coils were dirty and theyíre pretty clean. One thing I noticed today is that the blower will run for a minute or two and then stop running but everything else sounds like itís still running which is why I think the coils are freezing. When looking around at the blower I do hear a humming noise so not sure if itís a capacitor. The motor on the blower doesnít seem hot either. Any help would be greatly appreciated.
 
  #2  
Old 08-07-19, 08:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,641
Received 3,324 Upvotes on 2,985 Posts
Welcome to the forums.

The system charge has no affect on the blower. If the blower is stopping...... the coil will freeze.
You need to determine if your blower uses a capacitor. If it's a high efficiency unit.... it may use an electronic variable speed motor.

On further checking..... your air handler does use an ECM motor. There will not be a replaceable cap. That is an expensive motor and be under warranty on your unit. The link is the motor.

ECM motor
 
  #3  
Old 08-07-19, 08:29 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you for the reply, luckily my warranty expired about three months ago. Is there any way to directly test the blower to determine if it actually needs replacement?
 
  #4  
Old 08-08-19, 05:22 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
So I replaced the blower with a new one, but it seems the blower is not pushing much air even still.
 
  #5  
Old 08-08-19, 05:30 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,641
Received 3,324 Upvotes on 2,985 Posts
Was it the ECM type motor ?
The motor should have been $500 or more.
 
  #6  
Old 08-08-19, 05:44 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Itís the mot13906, verified that I replaced the same model. Was $219.
 
  #7  
Old 08-08-19, 06:02 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
The buzzing noise is still coming from something though itís a basler electric class 2 xfmr, appears to be a transformer.
 
  #8  
Old 08-08-19, 06:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,641
Received 3,324 Upvotes on 2,985 Posts
A buzzing transformer is not abnormal..... annoying though. It's possible it's not mounted tightly. Try rapping on it with a screwdriver and see if the hum changes.

Did you give the place you bought the motor the full model number ?
I believe the motor needs to be programmed for a particular unit.
 
  #9  
Old 08-08-19, 07:20 PM
R
Member
Thread Starter
Join Date: Aug 2019
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yeah I did. Appears to work better than the last one just not putting out a lot of air for some reason.
 
 