Central A/C stops cooling when outside temp is above 43 C

Reply

  #1  
Old 08-16-19, 02:04 AM
Member
Thread Starter
Join Date: Aug 2019
Posts: 1
Upvotes: 0
Received 0 Votes on 0 Posts
Central A/C stops cooling when outside temp is above 43 C

First of all, I live in Dubai, UAE.

We've been living in our current house since 2003 and it was not like this before. Basically, when the outside temperature goes above 43 C or so, my room's central A/C stops cooling (but the A/C fan continues to run) and starts blowing normal temperature air. The cooling in the other rooms in the house remains fine though (the other rooms have their own A/C compressor and thermostat). I've had this problem for the past 4 years/summers and the maintenance guys have been changing parts and whatnot over the years which result in no improvement. When the outside temperature goes below 43 C or so, cooling starts again.

Recently, the maintenance guys cleaned the outdoor unit, indoor unit, replaced the capacitors, and the contactor.

I found a thread that deals with the exact issue I am having but no solution is provided in the thread: https://www.doityourself.com/forum/a...isde-help.html

When it is hot outside, the compressor may turn on for like 30-40 seconds but then turn off again.

Any ideas?
 
Sponsored Links
  #2  
Old 08-16-19, 03:57 AM
the_tow_guy's Avatar
Group Moderator
Join Date: Feb 2001
Location: SW Fla USA
Posts: 11,789
Received 26 Votes on 23 Posts
I'm adding in the temperature conversion so posters won't have to look it up:

43C = 109F

 
  #3  
Old 08-16-19, 06:45 AM
Member
Join Date: Jun 2012
Posts: 886
Upvotes: 0
Received 2 Votes on 2 Posts
I had an old Carrier that shut down a few times when the temps were over 100F. It had started just after my spring tune up, where additional refrigerant was added. Turned out that the charge was too much and the added pressure when it got really hot was shutting the compressor down on thermal overload. I'd suggest having the charge checked when it's nice and hot outside.
 
  #4  
Old 08-16-19, 09:58 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,892
Received 257 Votes on 242 Posts
They need to......
1) check the refrigerant charge. Too high of a charge will cause the unit to overheat.
2) check the line voltage and current draw when running. A voltage sag will cause the unit to shut down.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: