A/C & heater running at same time?
Good afternoon all,
I really need some help with this. I'm living in Dallas, TX and am having an extremely difficult time with my AC. Recently my complex management has installed a brand new unit outside but we didn't notice any performance improvement with the new one. The air is blowing into the apartment pretty warm at all times of the day. The AC is set to cooling at 73 but it just doesn't seem to be able to get there.
Additionally, at my breaker panel, I have a 40A Breaker labeled heat and a 20A labeled AC. If I turn off the heat the entire unit stops working. But if I turn off just the AC the unit keeps running.
According to my wiring for the thermostat, I have an RH/RC jumper with a single red wire. See picture attached.
I am wondering what I can do in this situation or if there is maybe a possible short somewhere? I appreciate any help I can get with this.
I really need some help with this. I'm living in Dallas, TX and am having an extremely difficult time with my AC. Recently my complex management has installed a brand new unit outside but we didn't notice any performance improvement with the new one. The air is blowing into the apartment pretty warm at all times of the day. The AC is set to cooling at 73 but it just doesn't seem to be able to get there.
Additionally, at my breaker panel, I have a 40A Breaker labeled heat and a 20A labeled AC. If I turn off the heat the entire unit stops working. But if I turn off just the AC the unit keeps running.
According to my wiring for the thermostat, I have an RH/RC jumper with a single red wire. See picture attached.
I am wondering what I can do in this situation or if there is maybe a possible short somewhere? I appreciate any help I can get with this.

Last edited by PJmax; 08-19-19 at 11:09 AM. Reason: reoriented/resized picture
#2
Do you know if the outside unit is straight AC or is a heat pump? If a heat pump you don't have enough wires at the thermostat.
40 amp breaker for heat is normally controlled by the white wire. Move it to W1 assuming no heat pump.
40 amp breaker for heat is normally controlled by the white wire. Move it to W1 assuming no heat pump.
#3
Member
Thread Starter
Join Date: Aug 2019
Location: United States
Posts: 4
Likes: 0
Received 0 Likes
on
0 Posts
I believe this unit has a heat pump. Here is the part number: GSX140301KC
This is the website for the unit itself:
https://www.goodmanmfg.com/products/.../14-seer-gsx14
Also, attached is a photo for reference. Again, I believe this does have a heat pump, but I did not see a horizontal copper bar inside the unit.
This is the website for the unit itself:
https://www.goodmanmfg.com/products/.../14-seer-gsx14
Also, attached is a photo for reference. Again, I believe this does have a heat pump, but I did not see a horizontal copper bar inside the unit.

Last edited by PJmax; 08-19-19 at 11:13 AM. Reason: reoriented/resized picture
#5
Member
Thread Starter
Join Date: Aug 2019
Location: United States
Posts: 4
Likes: 0
Received 0 Likes
on
0 Posts
Wire moved to W1. Is there anything I need to watch out for or monitor? Or even might notice? Thank you for the help by the way.
Last edited by BMaverick; 08-18-19 at 01:01 AM.
#7
Member
Thread Starter
Join Date: Aug 2019
Location: United States
Posts: 4
Likes: 0
Received 0 Likes
on
0 Posts
I toggled to heat and the heater 100% turned on. It had that unique heater smell and the air was much much hotter. It was already 80 in the apartment when we woke up this morning too. We also called emergency maintenance out and they said there was nothing wrong with it.
#9
Hi, who wired that Tstat? Is that yellow conductor under the terminal screw for Y1, I would pull that cable out of the wall a bit and make sure there is nothing shorted there, I can see bare copper on the Red conductor .
What model # is that Tstat, does it require the C conductor?
Geo
What model # is that Tstat, does it require the C conductor?
Geo