Blower Running Constant

We had a recent lightning storm pass and nearby ground strikes damaged several electronics in my home. Here are some details I'm hoping to resolve:
  • Problem: blower runs constant, regardless of settings at the thermostat
  • Lennox residential system - approx. 16 months old
  • Single unit, zoned in a 2-story home (upstairs + downstairs)
  • Replaced the zone board (HZ311)
  • Should I:
    • Replace the capacitor on the ECM motor (attached: 100600-02)
    • Replace the transformer (attached: 42J3201)
  • Do you suggest I troubleshoot anything else? (ie: control board in the air handler)
Thank you, in advance, for any assistance/recommendations!

Shawn.
 
Attached Images   
Sponsored Links
  #2  
Old 08-20-19, 06:26 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 53 Votes on 46 Posts
Replace the capacitor on the ECM motor (attached: 100600-02)
No.

Replace the transformer (attached: 42J3201)
Only if it is not putting out 24 volts (aprox)

If you disconnect the thermostat red wires at the furnace does it stop?
 
  #3  
Old 08-20-19, 06:40 PM
Member
Join Date: Oct 2016
Posts: 1,304
Received 32 Votes on 29 Posts
Test for a call for the blower with your meter.
It’s likely either the thermostat or control board. A quick test with a meter will show what’s going on.
The parts you pictured have no effect on your problem.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: