I have an old Trane XL90 furnace/AC unit. The fan runs but you the condenser never kicks in to pump cool air. Where do I start to trouble shoot before calling a pro? Thermostat, outside unit, etc?

 
  #2  
Old 09-12-19, 02:43 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,614
Received 3,321 Likes on 2,983 Posts
Most likely the problem will be outside. There could be one of a number of problems.
1) Low on refrigerant
2) Tripped breaker to condenser or blown fuse in disconnect. (some have fuses.... some don't.)
3) Set the unit to a call for cooling and see if the contactor is closed. The contactor can be found in the wiring compartment where the wiring connects to the unit.

A meter would be very helpful in locating a problem.
 
 