Air Handler Not Blowing At All
I have an Airtemp AC system with the air handler in the attic. This is the second issue I have had with it. First few months board went and was blowing hot air. Today I found the outside unit running, but not the air handler. I had my attic air sealed and and reinsulated in July. I went up there tonight and found water in the overflow pan, but also blown in cellulose. I hit the breaker and tried to see if it would restart, but nothing. Water in overflow pan not high enough to get to drain, but I pushed a screw into drain to see if it was clogged. Too tight in my attic as my roof is a 4 pitch and the morons who installed first system put air handler very close to eave instead of under the ridge. That is all the info I have. Am I looking at needing to clear a drip line, bad board, bad motor? The guys who installed my system won't call me back until Monday at the earliest. System is only 3 yrs old. Gotta hope the rain kills this humidity and gets it below 80 so I can sleep tonight. Any thoughts would be helpful.
#3
Member
Is the condenser running? Is there power to the blower motor? Is there an overflow switch? Is it open or closed?
#4
Member
Thread Starter
Join Date: Jan 2017
Location: USA
Posts: 40
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Condensate line was clogged causing the safety switch to shut down air handler. I used my shop vac to suck down the blockage and A/C has caught up and house is back to normal. Thanks for the help.