Novel approach to oversized A/C blower?

I have a 1600 sq. ft. loft with 15 ft. ceilings and an open layout. When our 3.5 ton Trane unit died on us about 2 years ago, we had an AC Guy install a new 5 ton Trane. He didn't change the ductwork or turn the blower down just installed the unit and left.

Needless to say, our ducts are too small for the pressure and the entire system is REALLY loud. Like so loud you can't talk on a phone even though the vents are 13 ft. above your head. It cools great but it's unbearably loud.

I have asked three different AC guys to come out and quote me on new ductwork figuring it couldn't be too difficult of a job since all the ductwork is easily accessible and exposed. Nobody has gotten back to me--they are all too busy and apparently ductwork is the least enjoyable part of the job.

Finally, I had a young guy come in and quickly assessed the problem and came up with a brilliant solution. Or at least it sounds brilliant to me.

At the main output duct, he's going to punch a 12" hole and connect a 12" piece of a flexible duct that will connect to a Honeywell, variable static pressure controller on the input side. Then the output from the controller will reconnect on the input for the system. Kind of like a loopback from output to controller to input.

This gives us a lot more air moving through our system, lowering the pressure through our main ducts. And this can be turned up or down depending on how cold we want it, how quiet, etc.

It will also ensure a source of air going to the input supply in case something were to cover the vent and no air could get into the unit. Plus the new air will already be conditioned so it will make the air colder.

He says this will extend the life of my 5 ton unit because it is having to do so much work to pull air through a tiny supply and push it out tiny ducts to vents.

Is this a viable solution? Anything I need to be careful of? Thanks in advance for your help.
 
Sponsored Links
  #2  
Old 10-10-19, 09:16 AM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 4,780
Received 141 Votes on 131 Posts
I'd just turn the blower speed down and be done with it!
 
  #3  
Old 10-10-19, 09:21 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,143
Received 473 Votes on 444 Posts
Good question on how that will work.
You can't just slow the fan down or the coil will freeze up.
 
  #4  
Old 10-10-19, 12:20 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,795
Received 8 Votes on 8 Posts
That 12in flex duct will only move 390cfm at .08 static. Your duct will still be under sized a ton. Plus you are going to short cycle the unit so you are going to work the equipment harder not easier. You might have freezing issues as well. Has anyone done a heat load to see the exact size of unit you actually need?
 
  #5  
Old 10-10-19, 06:51 PM
Member
Join Date: Oct 2016
Posts: 1,556
Received 53 Votes on 49 Posts
What was the reasoning to begin with in changing the 3.5 to a 5 ton?
Even if the duct is fixed the unit will likely short cycle itself to death.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: