Electrical issue at disconnect

I'm either getting no voltage or really high voltage at the disconnect, it's never the same. Once in awhile I get the proper voltage. I replaced and tested the circuit breaker and it has the proper voltage. So I'm not sure if my issue is the disconnect itself or between there and the breaker. The wires are all tight going into the disconnect. One of the prongs on the pull out is really chewed up also.
 
  #2  
Old 11-23-19, 06:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,630
Received 3,323 Likes on 2,984 Posts
Welcome to the forums.

I suspect a meter problem. if there was a neutral involved....... I'd say it was a neutral problem. However..... you are working with an A/C condenser that doesn't require a neutral. That means you should measure 240v.... never higher than that.

Your disconnect has two wires in and two wires out. You should measure the in and out wires with the disconnect pull-out in place.
 
  #3  
Old 11-24-19, 11:21 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,872
Received 226 Likes on 200 Posts
PJmax, how did you know there was a A/C condenser involved?
 
  #4  
Old 11-24-19, 11:41 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,630
Received 3,323 Likes on 2,984 Posts
The member posted in the air conditioning forum.
 
 