Replacing GE weathertron thermostat with a Honeywell 6000

I am replacing a weathertron for a Honeywell 6000. The old terminals are R, W, T, B, X2, G, O, and Y. New terminals are L, Aux/E, G, O/B, C, Y, and R. I plan to connect R to R, Y to Y, B to C, O to O/B, G to G, and terminate the old T. That leaves me with the old W and X2. Assuming they are for Heat and emergency heat, where do I land them on the new thermostat? My system is an old GE heat pump with a plus 1 kit and a gas furnace. I figured W would go to Aux and X2 would go to E but there is only one terminal marked Aux/E
 
  #2  
Old 01-20-20, 03:21 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,798
Received 83 Upvotes on 75 Posts
Easiest should be to put both wires in the aux/e terminal.
 
  #3  
Old 01-20-20, 09:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,663
Received 3,328 Upvotes on 2,987 Posts
On the old stat..... X2 is emergency heat and W is the AUX heat.
Most systems the X2 and W are connected together at the air handler.

If you can't fit both wires in your new stat..... use just the W wire.
 
 