Ac unit not getting 24v

Not getting 24v at the contactor on my ac unit. Ive checked the thermostat and it's getting 24v on all wires. Had a checkup on my air handlers a couple of months ago and maybe they knocked a wire loose. In the picture below the white loose wire runs to the outside condenser unit. Just not sure which port to connect it bad too. Hope this makes sense.
 
Attached Images  
  #2  
Old 04-01-20, 02:39 PM
B
Member
Thread Starter
Join Date: Apr 2020
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also the red wire connected on the Y terminal also goes to the outside unit.
 
  #3  
Old 04-01-20, 03:21 PM
D
Member
Join Date: Feb 2015
Location: US
Posts: 8
Upvotes: 0
Received 4 Upvotes on 4 Posts
2 wires from condensor

One will go to Y and the other to C.
 
  #4  
Old 04-01-20, 03:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Welcome to the forums.

The white wire from the outside condenser goes to the C terminal.
 
  #5  
Old 04-01-20, 04:00 PM
B
Member
Thread Starter
Join Date: Apr 2020
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Worked! Sure appreciate it fellas! Stay safe
 
 