No 24V from T2(Defrost board) so contactor won't engage

So Contactor is working fine. I checked it bypassing 24V.

T1 and T2 is not getting 24V. What could be the problem?

and also if I manually engage Contactor by pushing it, the Fan does not work.. Is it because of bad capacitor?
 
Attached Images    
  #2  
Old 05-13-20, 01:54 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,798
Received 83 Upvotes on 75 Posts
If you have 24vac on Y but 0 on T1 then the pressure switch is open. You need to call a HVAC tech.

The contactor is for the compressor, not the fan as the board controls that.
 
PJmax voted this post useful.
 