Solving condensate line/overflowing issues
#1
Member
Thread Starter
Solving condensate line/overflowing issues
I looked up at the ceiling on my second floor the other day and noticed it was wet.
The condensate line clogged last year so I kind of know what to expect. I should also say, I'm coming around to the fact that I'm going to need to replace this entire system soon. It didn't hold pressure when I had a company out to inspect it several years ago, I don't know how it's held out this long. I'm deciding between just replacing the condenser (where I assume the leaks are, but it's r22) or the entire system (but I'm dreading the air handler/attic portion of the job).
I'm going to at least start to handle the problem tomorrow. I bought a drain clearing gun this time (it sucked last year trying to figure out how to snake the 3/4" pvc with sharp 90s) and tablets that should deal prevent/deal with the scum buildup over the next several months.
I'm start this thread off of memory because I want to have game plan going up there. Crawling around my attic to deal with this sucks, no room to stand up, crawling around in fiberglass, no room to stand, it's hot.
I attached a picture of the air handler that I took several years ago when I renovating the system (and installing attic insulation). Unfortunately, I can't find the model number, I'm going to get it tomorrow.
Anyway,
1. Inside of the air handler there is no real drip pan. It's lined in fiberglass that's saturated with water and then sort of drains out of the PVC (but the fiberglass stays saturated), is that normal?
2. Since the air handler draws air in (and all openings need to be taped so as not to suck in attic air/dust)...does that mean that air currently gets sucked in from the outside through the drain line?
3. I'm considering adding a full drip pan underneath the unit. Since it doesn't seem to be designed for it, would it be worth it?
4. Last year I installed a condensate overflow switch, so I didn't think I would have this issue again (at least not without the A/C shutting off), but clearly something isn't working properly (again, I'm going to investigate tomorrow).
5. If I replace the entire system, is replacing the attic unit going to be be as bad as I fear? I want to tell the HVAC company we would hire that I would handle the attic portion of the job to 1. keep costs in check and 2. because I don't trust anyone else to minimize damage/repairs/insulation work/etc. and not be tracking crap through my house. I would invest in HVAC press or crimp jaws for the copper portion of the job.
Thank you


I'm going to at least start to handle the problem tomorrow. I bought a drain clearing gun this time (it sucked last year trying to figure out how to snake the 3/4" pvc with sharp 90s) and tablets that should deal prevent/deal with the scum buildup over the next several months.
I'm start this thread off of memory because I want to have game plan going up there. Crawling around my attic to deal with this sucks, no room to stand up, crawling around in fiberglass, no room to stand, it's hot.
I attached a picture of the air handler that I took several years ago when I renovating the system (and installing attic insulation). Unfortunately, I can't find the model number, I'm going to get it tomorrow.
Anyway,
1. Inside of the air handler there is no real drip pan. It's lined in fiberglass that's saturated with water and then sort of drains out of the PVC (but the fiberglass stays saturated), is that normal?
2. Since the air handler draws air in (and all openings need to be taped so as not to suck in attic air/dust)...does that mean that air currently gets sucked in from the outside through the drain line?
3. I'm considering adding a full drip pan underneath the unit. Since it doesn't seem to be designed for it, would it be worth it?
4. Last year I installed a condensate overflow switch, so I didn't think I would have this issue again (at least not without the A/C shutting off), but clearly something isn't working properly (again, I'm going to investigate tomorrow).
5. If I replace the entire system, is replacing the attic unit going to be be as bad as I fear? I want to tell the HVAC company we would hire that I would handle the attic portion of the job to 1. keep costs in check and 2. because I don't trust anyone else to minimize damage/repairs/insulation work/etc. and not be tracking crap through my house. I would invest in HVAC press or crimp jaws for the copper portion of the job.
Thank you

#2
If the air handler is R-22...... replace the entire system.
There are two drain lines on an air handler. One is always lower than the other. The lower drain is the primary drain. The upper drain is the overflow. Connecting them together like you have there is wrong. It's not always easy to see but one drain is lower. The idea is when the lower drain clogs..... water comes out the upper drain. In your case.... the float should be on the upper drain and it should not be connected.
There are two drain lines on an air handler. One is always lower than the other. The lower drain is the primary drain. The upper drain is the overflow. Connecting them together like you have there is wrong. It's not always easy to see but one drain is lower. The idea is when the lower drain clogs..... water comes out the upper drain. In your case.... the float should be on the upper drain and it should not be connected.
#3
Member
Thread Starter
Yeah, I couldn't imagine them being piped together was correct. Now I have to decide if I struggle to add a second drain tomorrow or not...I probably won't though with the goal being to replace the system in the fall and add it when I have more room to work.
But the fiberglass sitting in the condensation/water on bottom of the pan is normal?
But the fiberglass sitting in the condensation/water on bottom of the pan is normal?
#4
No.... there should be nothing in the condensate pan but water.
You don't need to run a second line. Disconnect the secondary drain and use it for a float switch only.
Clean the primary drain. One way that many people clean the line is to suck it out from the outside.
You don't need to run a second line. Disconnect the secondary drain and use it for a float switch only.
Clean the primary drain. One way that many people clean the line is to suck it out from the outside.
#5
Member
Thread Starter
Ty, I'll take a lot more pictures tomorrow.
And I understand, I guess I bought/installed the wrong type switch. Rather than threading into the drain port it clamped on to the side of the drip pan. Will know more about the issue tomorrow.
And I understand, I guess I bought/installed the wrong type switch. Rather than threading into the drain port it clamped on to the side of the drip pan. Will know more about the issue tomorrow.
#6
That type of switch is used if you have a second drip pan underneath your air handler.
You want something more like in the link. With this type of switch.... it could be removed and a few cups of bleach and hot water could be poured in to flush the pan.
Float switch
You want something more like in the link. With this type of switch.... it could be removed and a few cups of bleach and hot water could be poured in to flush the pan.
Float switch
#7
Member
Thread Starter
So the air handler model is FB4ANA036. From what I can tell this is a 3-ton air handler? Using the sizing guide here, https://hvacdirect.com/sizing-air-co...nd-heater.html, I was thinking I would only need a 1.5 ton system (for an approximately 1000 sq ft area). Have things changed in 40 years (something I found googling said 1982) or was this just installed way oversized? A little more information about the system, there (6) supply ducts and only (1) 2'x2' return on the second floor (at the top of the stairs) - There is lots of positive pressure in the bedrooms lol.
Anyway the leak seems to be from the bottom of the plastic drain pan, it must be cracked :/ glad I've come around to a new system...temporarily I just bent some aluminum flashing I had as a drip tray and have it (more) safely dripping into a 5 gallon bucket in the closet through the access hatch.
Anyway the leak seems to be from the bottom of the plastic drain pan, it must be cracked :/ glad I've come around to a new system...temporarily I just bent some aluminum flashing I had as a drip tray and have it (more) safely dripping into a 5 gallon bucket in the closet through the access hatch.
#8
Can't comment on the chart as we don't know where you live.
I would agree that 3 ton seems a little large.
I'd probably go with a 2 ton system.
The size of the system needed is based on heat load.
If you're going to have the system installed get a free quote with proper sizing.
I would agree that 3 ton seems a little large.
I'd probably go with a 2 ton system.
The size of the system needed is based on heat load.
If you're going to have the system installed get a free quote with proper sizing.
#9
Member
Thread Starter
I live in Bergen County, NJ, so the green area according to the sizing guide (https://hvacdirect.com/sizing-air-co...nd-heater.html) (although I'm sure you're aware of it being from "Northern NJ" lol
I think I'm going to do the job myself in the fall (other than the reclaiming and adding of refrigerant).
I think I'm going to do the job myself in the fall (other than the reclaiming and adding of refrigerant).
#10
Hi, I would say good luck installing it yourself and having some else charge it, better find someone willing to do that before you do the work.
Geo
Geo
#11
Member
Thread Starter
Lol yeah I was wondering how big of an issue would that be...I feel like there's gotta be someone willing to make money doing it (in the off season). I also probably know someone who would do it through my job as a fire sprinkler contractor.
#13
Member
If your immediate problem is a leaking drip pan that aluminum flashing won't correct you may wish to check this link. https://www.repairclinic.com/PartDet...-75102/4869099 .
Personally I quit working HVAC units in attics years ago, regardless I would be critical of spending time and money on an old R-22 system that may have condenser issues as well. BTW, enter your model number yourself to confirm it is in fact the part you need. The one comment/review left is confusing.
Personally I quit working HVAC units in attics years ago, regardless I would be critical of spending time and money on an old R-22 system that may have condenser issues as well. BTW, enter your model number yourself to confirm it is in fact the part you need. The one comment/review left is confusing.
#14
Member
Thread Starter
Originally Posted by PJmax
It's more than a DIY job. It requires some specialized tools, a pump, nitrogen and gauges.
But installing the units themselves and soldering a couple of connections doesn't seem bad. I've never solder copper pipe before but I'm an adept electronics solderer and youtube couldn't make it look easier! lol I'm excited to give it a shot. Other than the attic portion that sucks because of working conditions, the rest of job seems pretty easy...
Originally Posted by fastback
If your immediate problem is a leaking drip pan that aluminum flashing won't correct you may wish to check this link. https://www.repairclinic.com/PartDet...-75102/4869099 .
Personally I quit working HVAC units in attics years ago, regardless I would be critical of spending time and money on an old R-22 system that may have condenser issues as well. BTW, enter your model number yourself to confirm it is in fact the part you need. The one comment/review left is confusing.
Personally I quit working HVAC units in attics years ago, regardless I would be critical of spending time and money on an old R-22 system that may have condenser issues as well. BTW, enter your model number yourself to confirm it is in fact the part you need. The one comment/review left is confusing.
#15
Member
Soggy pink insulation has to go. I understand those helping you on this site are far more qualified than I. However, I don’t understand why there is wet insulation lying in the drainage sump area. This needs to be resolved or you will continue to have condensation drainage issues. This pan needs to be relatively clean so water can flow to the drain.
I would resolve this first, then work on clearing blockages in the drain line. This year. You can deal with whether to replace the system later, fix drainage now.
Am I missing something here?
I would resolve this first, then work on clearing blockages in the drain line. This year. You can deal with whether to replace the system later, fix drainage now.
Am I missing something here?
#16
Member
Thread Starter
Originally Posted by clancy
Soggy pink insulation has to go. I understand those helping you on this site are far more qualified than I. However, I don’t understand why there is wet insulation lying in the drainage sump area. This needs to be resolved or you will continue to have condensation drainage issues. This pan needs to be relatively clean so water can flow to the drain.
I would resolve this first, then work on clearing blockages in the drain line. This year. You can deal with whether to replace the system later, fix drainage now.
Am I missing something here?
I would resolve this first, then work on clearing blockages in the drain line. This year. You can deal with whether to replace the system later, fix drainage now.
Am I missing something here?
There is small 48" x 27" pan I would like to use, but my current air handler (and carrier units in general) appear to by 50" long.