Trane xe1200 common wire location and color
Received 0 Votes
Trane xe1200 unit side t-stat plug
Hello, I have a trane xe1200 roof mount unit with heat pump. I am trying to add a smart thermostat but I cannot find a “white” common wire in the board up in then unit.
Normally you would find a t-stat wire block section with matching letters to simply add the common wire, but this unit has a “plug/socket” instead that connects into the board but it has no lettering/ diagram to describe the wires.
Is anyone familiar with unit and could advise on the color or location of the common wire. Thanks a million!
wire colors at socket plug:
red -used = Red t-stat
yellow -used. = yellow t-stat
orange -used = blue t-stat
black - used = green t-stat
blue - not used/hooked up
brown 1- not used/hooked up
brown 2 - not used/hooked up
brown 3 - not used/hooked up
Not making sense to me. That is a defrost control board for a heat pump. You don't connect the thermostat to it - you connect the thermostat to the air handler and then wire the air handler to the heat pump.
That said, if you look at the board there is a "B" next to the blue wire so that is common. Trane uses B instead of C labeling.
Received 0 Votes
Additional pics
Thank you for the input. I followed the t-stat leads back to that socket. I am adding some additional pics for reference.
when you say the blue wire has a “B”, whee do you see that?
Hi, there is a transformer on the left side of that cabinet, it should have 4 terminals , 2 will be 120VAC and 2 should be 24 VAC , do you have a meter? one side of the 24 volts should be Common “B” , it may also connected to cabinet, is there a wiring Dia. You can post?
Geo🇺🇸
Geo🇺🇸
Is this a packaged heat pump system...... everything is on the roof ?
I'm seeing this as a split system.
That means your thermostat wiring is not there..... it's located inside where the air handler is.
Confusion as XE 1200 is normally used for split systems.
From model number (WCP048F100AA) that is a packaged unit. Literature shows that there should be a loose blue common (B) in the lower section. You can see it in the pic with the thermostat wires there is an unused blue wire there.
https://www.trane.com/webcache/wcp-iom-1e_12012003.pdf