Climate Master 27seer tranqulity geo thermal unit not cooling

Somethings not quite right with my unit that is about 8 years old. Its blowing air but its just not cold. Ive determined the pumps arent running as there is no vibration on them. If I pull the breakers and "reboot" the unit - when it kicks on everything is good and it blows cold air (65 at the register) - it quits after about an hour or so. The first time I did this a week ago it worked that long, the past couple days it'll only run for an hour with cool air. When I notice its not cold air I notice the pumps arent running and neither is the compressor. After a reboot I can hear and feel the compressor kick on and things are good, until they arent.
Any way to pull diagnostic codes or something to see if I need a new compressor or something?
 
  #2  
Old 07-05-21, 11:05 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,139
Received 3,619 Upvotes on 3,245 Posts
My forum partner is familiar with geo systems. I am not. I know how they operate but not their individual problems.

You have a sophisticated system that requires circulating water system maintenance. I would hope you have an experienced service company that maintains your system.

I can help you but I need a model number of your systems air handler.
 
  #3  
Old 07-05-21, 11:28 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,475
Received 89 Upvotes on 82 Posts
That unit will go into a hard lockout if the internal condensate overflow detects a backed up drain.
It sounds like you need to clear the drain.

A good test is to pour water into the primary drain pan. It is the top panel on vertical models.

You can pull up trouble codes by jumping the 2 TEST terminals on the control board.
Count the flashes.
1- no fault
2-high pressure lockout
3-low pressure
4- freeze protecting sensor 1 lockout
5- freeze protector 2 lockout
6- drain lockout
7 - over/under voltage
8-UPS
9- swapped thermister

Reset power to exit.

It is hard to see the test pins. I have trouble and I know that they are there.
 
PJmax voted this post useful.
 