Finally Mini-split!
#1
Finally Mini-split!
I'm sure many of you have seen my many many threads on that Mitsubishi Electric Mini-Split?
#1
#2
#3
Well they finally got it fixed!
Well I have only been complaining for what two years!!!!
Anyway back in August it was not doing much of anything (other then wasting electricity that I pay for)
So they sent a real tech and as I was saying all along it was low on refrigerant (R-410A) it had practically nothing in there! The fittings (all 4) were only hand tightened so it leaked out!
Anyway is checking the pressure the proper way to charge it? As that is all the tech did the older dial gauges and a pink container of R-410A. At the time the outside was around 83° F as soon as he put it in the air started getting a lot colder even colder then when it was installed by the idiots in mid 2017!
I thought they also had to go by Sub-cool and Super-heat and other measurements of then pressures?
#1
#2
#3
Well they finally got it fixed!
Well I have only been complaining for what two years!!!!
Anyway back in August it was not doing much of anything (other then wasting electricity that I pay for)
So they sent a real tech and as I was saying all along it was low on refrigerant (R-410A) it had practically nothing in there! The fittings (all 4) were only hand tightened so it leaked out!
Anyway is checking the pressure the proper way to charge it? As that is all the tech did the older dial gauges and a pink container of R-410A. At the time the outside was around 83° F as soon as he put it in the air started getting a lot colder even colder then when it was installed by the idiots in mid 2017!
I thought they also had to go by Sub-cool and Super-heat and other measurements of then pressures?

Top Answer
09-16-21, 07:25 PM
Reading your list of posts it seems as though your idea in #1 may have worked?
I won't be going into charging a system to much other than saying analog gauges, a temperature probe, and the ability to add/subtract will give the figures you mentioned. Digitals are more convenient as they do the math for you. I wouldn't judge a tech by what they are comfortable using vs what you perceive to be improper. Judge them instead on their results. There is at least one other way to properly do the job relying on primarily an even different piece of equipment.
Hope you system continues to perform properly for you. If it did leak out, without help, then you probably still have a leak.
I won't be going into charging a system to much other than saying analog gauges, a temperature probe, and the ability to add/subtract will give the figures you mentioned. Digitals are more convenient as they do the math for you. I wouldn't judge a tech by what they are comfortable using vs what you perceive to be improper. Judge them instead on their results. There is at least one other way to properly do the job relying on primarily an even different piece of equipment.
Hope you system continues to perform properly for you. If it did leak out, without help, then you probably still have a leak.
#2
Member
Reading your list of posts it seems as though your idea in #1 may have worked?
I won't be going into charging a system to much other than saying analog gauges, a temperature probe, and the ability to add/subtract will give the figures you mentioned. Digitals are more convenient as they do the math for you. I wouldn't judge a tech by what they are comfortable using vs what you perceive to be improper. Judge them instead on their results. There is at least one other way to properly do the job relying on primarily an even different piece of equipment.
Hope you system continues to perform properly for you. If it did leak out, without help, then you probably still have a leak.
I won't be going into charging a system to much other than saying analog gauges, a temperature probe, and the ability to add/subtract will give the figures you mentioned. Digitals are more convenient as they do the math for you. I wouldn't judge a tech by what they are comfortable using vs what you perceive to be improper. Judge them instead on their results. There is at least one other way to properly do the job relying on primarily an even different piece of equipment.
Hope you system continues to perform properly for you. If it did leak out, without help, then you probably still have a leak.
CircuitBreaker,
PJmax
voted this post useful.
#3
I won't be going into charging a system to much other than saying analog gauges, a temperature probe, and the ability to add/subtract will give the figures you mentioned. Digitals are more convenient as they do the math for you. I wouldn't judge a tech by what they are comfortable using vs what you perceive to be improper. Judge them instead on their results.
Well it is working fine even better then when it was put in!
I think it leaked out as the fittings were never tightened only barely threaded on by hand!
He said this is the 4th one he fixed with the same issue. 186 apartments and he did 4 already!
I don't care if it continues to work beyond the Summer of 2022 as I'm leaving this dump of a place soon anyway for this and many other issues!
#5
Member
And a scale was the "different piece of equipment" I was referring to. I didn't know if that would be jumping into an area to be avoided.
#6
Minis must be charged via weight. Not pressure.
What about any that did not go AWOL how is that calculated in the weight added not asking step by step just what is needed?
Edit:
I don't care if the tech was correct all I care about as it works (for now) He also tightened all 4 fittings. The indoor was a PITA and a Half to get to as well!
#7
Member
All manufacturers have a formula for additional refrigerant to add per extra foot of lineset length. They come precharged, that weight is listed on the outdoor unit.
#8
All manufacturers have a formula for additional refrigerant to add per extra foot of lineset length. They come precharged, that weight is listed on the outdoor unit.
Well on the cooler days it is doing the same thing as it did before

I don't know he just connected a green jug to the low side (Looked like a green propane tank) and stopped when it started getting cold and the pressures were within what he said was OK?
#9
Member
Improper charging procedure. That’s likely why it’s still not working correctly.
There is no “correct operating pressure” on an inverter drive mini.
There is no “correct operating pressure” on an inverter drive mini.
CircuitBreaker
voted this post useful.
#10
There is no “correct operating pressure” on an inverter drive mini.
Is there an easy way to make it stay on all of the time? as in unplug a sensor (or that would probably make it error out and do nothing?)
Anyway I looked up "green refrigerant jug" and that is R-22 but this is an R-410A unit and why would they waste the good stuff on something that does not need R-22?
There is a sensor in front of the indoor heat exchanger that can be unplugged easily do you know what that is for?
they call them heat exchangers (at-least that what Mitsubishi Electric calls them in the service manual) now as it can be the evaporator or condenser depending on what mode it is in.
#11
Member
Green is R-22.
Pink is R-410A.
Sounds like the guy needs a class or two on how to service units.
There are certain charging procedures. But no way to charge by pressure even if it’s running flat out.
Pink is R-410A.
Sounds like the guy needs a class or two on how to service units.
There are certain charging procedures. But no way to charge by pressure even if it’s running flat out.
#12
Green is R-22.
He did say "This would make it way colder then it ever was"
it’s running flat out
I can be my own thermostat if it gets too cold I can just turn it off for a bit
#13
Member
He used the wrong refrigerant. It’s not that R-22 is “the good stuff”.
The oil in that compressor isn’t even comparable with R-22. The guy appears to have no clue what he’s doing.
Thermostat is needed. You can’t lock the thing on. That’s not how it works.
The oil in that compressor isn’t even comparable with R-22. The guy appears to have no clue what he’s doing.
Thermostat is needed. You can’t lock the thing on. That’s not how it works.
#14
He used the wrong refrigerant. It’s not that R-22 is “the good stuff”.
The oil in that compressor isn’t even comparable with R-22. The guy appears to have no clue what he’s doing.
The oil in that compressor isn’t even comparable with R-22. The guy appears to have no clue what he’s doing.
R-22 is the good stuff it is cold in a properly working system same with R-12. Also does not operate at such high pressures as R-410A does
Thermostat is needed. You can’t lock the thing on. That’s not how it works.
I'm jellious of the people who's portable or window AC had the compressor relay get stuck/welded on!
#15
Member
Did you put the R-22 in the unit?
Different refrigerants are different entities. One isn’t better then another. And they are not cross compatible. R-410A runs at the pressures it does because of its chemical makeup and operating parameters.
Same with R-12. It isn’t a cross replacement for R-22.
P/T chart isn’t even close. Wrong refrigerant will kill the unit.
Different refrigerants are different entities. One isn’t better then another. And they are not cross compatible. R-410A runs at the pressures it does because of its chemical makeup and operating parameters.
Same with R-12. It isn’t a cross replacement for R-22.
P/T chart isn’t even close. Wrong refrigerant will kill the unit.
#17
Did you put the R-22 in the unit?
Any updates? Does it actually have R-22 in it?
It has R-410A but apparently not enough as it still cuts off on low pressure switch activation on cooler days but outdoor temps below 55° I can just open the door with a fan on to keep comfortable but the 70° > when I really need it it works fine.
#18
Member

Is this the bottle that was used? Nothing green at all about R-410A. Reclaim bottles are gray and yellow. Low charge can also kill the unit. With poor compressor cooling and low oil return.
#19
Is this the bottle that was used? Nothing green at all about R-410A. Reclaim bottles are gray and yellow. Low charge can also kill the unit. With poor compressor cooling and low oil return.
I asked for clarification I called the guy (Not housing) he said had 2 containers in the cart he brought the green R-22 was for the older 10 years old (Dry shipped AKA no refrigerant inside at all) 2.5T AC in the office he had his van in the other area he only bought over a cart on wheels. He actually hooked the pink R-410A jug, I was not paying attention totally just thought I saw him hook up the green one.
R-410A is not green (very high global warming Potential) anyway more of a "stop-gap" for the new flammable stuff that is being used now such as R-600A R-290 R-32 R-1234YF and probably more now.
I still think it is a tad low someone told me years ago to put a blanket or towel over the back outdoor unit (Condenser in cool mode I used it in heat mode once I'll stick to my $ baseboard heaters) to raise the refrigerant pressure as the condenser stays hotter or something like this as they do this for charging in cooler weather known as a condenser blanket.
Will doing something like this long term (EX: not charging in cold weather) hurt it? I'm obviously not going to do this on hot summer days.
#20
Member
R-410A bottles are pink.
You can’t charge via pressure. He didn’t charge it right, and now it still doesn’t work before he didn’t charge it right.
No, the blanket idea will not work.
Since he found it low on refrigerant, where did he find the leak and has he fixed it yet?
You can’t charge via pressure. He didn’t charge it right, and now it still doesn’t work before he didn’t charge it right.
No, the blanket idea will not work.
Since he found it low on refrigerant, where did he find the leak and has he fixed it yet?
#21
Since he found it low on refrigerant, where did he find the leak and has he fixed it yet?
Anyone still make a decent window AC? That is what I'm going to do this summer as I'm tired of this issue.
I'm going to buy one now as I can get one cheaper then the summer rush prices.
Edit: If I buy one now can I safely test inside as long as the inside temp is not too cold for it to operate properly?