New A/C unit icing up


  #1  
Old 10-01-21, 12:38 PM
M
Member
Thread Starter
Join Date: Oct 2021
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
New A/C unit icing up

I've lived in my house for 6 years; in the past 6 months, both the compressor/air handler unit (in the attic) and the condenser (on a concrete pad outside) have been replaced. The copper tubing and inlet valve on the new condenser will ice up pretty heavily, but only if the return air filters are in place. If I take the return air filters out, there's some condensation (but I live in McAllen TX, in a very humid climate). As I said, I've lived in my house for 6 years, but this is a new problem. I've always previously been able to have the return air filters in place. Any ideas on what the underlying issue could be?
 
  #2  
Old 10-01-21, 12:58 PM
MyNextMover's Avatar
Member
Join Date: Oct 2021
Location: United States
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Check the drain from your unit snake it out. Probably clogged up
 
  #3  
Old 10-01-21, 01:22 PM
Marq1's Avatar
Member
Join Date: Sep 2016
Location: USA MI
Posts: 9,746
Received 1,210 Upvotes on 1,098 Posts
Freon has leaked out.

Refrigerant lines can kink, fans can stop moving, filters can become clogged, and things can leak. Any of these things causes a drop in pressure, allowing the refrigerant to expand too much and become too cold. ... A too-low level of refrigerant is also known to cause freezing up.
 
  #4  
Old 10-01-21, 03:25 PM
R
Member
Join Date: Oct 2016
Posts: 2,181
Received 197 Upvotes on 179 Posts
What air filter is being used?
 
  #5  
Old 10-01-21, 11:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,864
Received 3,749 Upvotes on 3,362 Posts
Welcome to the forums.

Wouldn't be a condensate drain issue.
Typically low on refrigerant would cause the evaporator to ice over.

Sounds like the system is very responsive to air flow. That's determined by filter/type, something put in front of the returns or registers closed down.

As roughneck mentioned.... what filters are you using ?
 
  #6  
Old 10-02-21, 06:43 AM
M
Member
Thread Starter
Join Date: Oct 2021
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
The new unit was installed three days ago, so I can rule out low refrigerant. I threw out the old return air filters and replaced them with the cheapest, thinnest ones I could find. Problem solved - no more ice.
 
  #7  
Old 10-02-21, 07:58 AM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,618
Received 74 Upvotes on 65 Posts
Just because the system was recently installed, I don't think you can assume that the correct amount of refrigerant was added. Years ago my son had central air (split system) installed. It wasn't cooling well at all. I told him to call the contractor and come back to determine why. It turns out they hadn't added the correct amount of refrigerant. After putting more in, the air coming out of the ducts was ice cold.
 
  #8  
Old 10-02-21, 08:11 AM
R
Member
Join Date: Oct 2016
Posts: 2,181
Received 197 Upvotes on 179 Posts
What air filter was being used to cause the icing.
Just because it is new, doesn’t mean it’s right. You are wrong to assume the charge is correct.
 
PJmax voted this post useful.
 