Old window unit short cycle

Window ac unit.

Off all day sat for years, is a 1992 coolerator. It was working seeming fine for a few days then recently turned it on, it cools for about 10 seconds and shuts down the compressor and cycles again after a minute.

I had the unit out, nothings frozen and as clean as I can get it.

Thermostat? Low Freon?
 
  #2  
Old 10-04-21, 08:08 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,159
Received 3,627 Upvotes on 3,251 Posts
Welcome to the forums.

Check the compressor. Is it getting hot to the touch ?
It sounds like it may be cycling from thermal overload.
Doesn't necessarily mean it's low on refrigerant. It could be a capacitor issue.
 
 