Looking at the nest thermostat with current working wiring..... the wiring doesn't match the control board.
Your stat has white on W1 which is usually correct but no white appears at the furnace from the stat.
At the furnace you have the blue wire on W1.
The red on Y and the white on C look like from the A/C condenser.
I have updated the photo to the correct wiring at the Amana unit.
The initial photo was for the Amana cooling the upstairs. I am working on the downstairs thermostat.
See if this makes better sense about where I may have gotten this wrong or what I can do to get this correct and operating.
The green wire on Y and the white wire on C go to the outside condenser.
I can't see the letters on the stat but it sounds like you have it connected correctly.
That's a mechanical stat. No programming.
Did you put the screws all the way in that hold the stat to the base ?
Try jumpering red to green. Does the blower start ?
If it doesn't... there is a problem at the air handler.
To add to what Pete said, if jumpering the red & green wires doesn't turn it on, it's possible that you may be missing the 24VAC (R to C). Did you turn off the power to the air handler before disconnecting the wires? If you didn't, the Red (24VAC) may have momentarily been shorted to the common, either blowing the fuse or possibly the transformer.
First, this group is amazing and I hope I can learn a few things.
I figured out my problem. I had power (tested this with my multi-meter) but also touched the red and green wire.
I had the access panel on the air handler off, and there is a switch located there and this was preventing things from turning "on."
Hi,
At my home the outside AC unit doesn't turn ON and the Air handler (inside unit) turns ON and the temperature goes way beyond the set temperature. Thermostat is set at 78 degrees and the actual temperature in home goes upwards over 80 and it shows on thermostat too. When I trip the AC and Air Handler's in the electric circuit breaker then both AC outside unit and Air handler turn's ON and the temperature comes down to the set 78 degrees. Can someone please let me know what could be the issue. This is happening almost every day.
Thanks,
Ven
Read More
Trying to replace a motor on a trane xe 800 weathertron heat pump. We are not sure where to plug in the new motor on the cap and contactor. The new motor has its own capacitor so we just need to know where the black wire and the white wire (purple on old motor) go.Read More