Hello to all and thanks for any help you can provide to me.
I have central (forced) air divided up into three zones in my home.
Zone 1 and zone 2 work fine and call for cool air (activate the compressor outside) when I lower the thermostat for that zone..
Zone 3 only turns on the blower. It does not activate the compressor. Also, the damper for zone three seems to be stuck open all the time. I will get cool air if Zone 1 or 2 call for cooling.
I have the common three zone panel made by Honeywell probably from the 1990's.
Are these two issues related or do I have two separate problems?
I'm a bit confused. Your initial reply stated it might be a board issue. Meaning the large control board correct?
I did try swapping one thermostat from one zone with this #3 zone. No change. All I get is air with no compressor running.
There are two leads that go to the damper for each zone. My thinking was these are 24v AC to the damper motor. Would reversing these AC leads cause the motor to run in the other direction?
When none of the zones are calling for cooling the damper output is 24vac all around and all three green LED's are lit. The yellow System LED of off.
When a zone calls for cooling, that zone damper goes to 0vac only, the green LED for that zone is lit and the others are off. The yellow System LED is also lit.
However, if zone 3 calls for cooling by itself, the yellow System LED stays off and I get no compressor.
The damper does go to 0vac (as it should ?) and Zone 3 green LED is on by itself.
So, my question is:
If the damper for zone 3 is jammed in the open or partially open state, will that prevent the compressor from coming on for that zone?
Located the three dampers in the ceiling. There is a large Allen head bolt that secures the entire box to the damper shaft. Loosening that and off it came in my hand,
I took it to my bench to have a better look.
Applying 25 volts AC the motor, it would rotate the mechanism to about 25% of the travel then bog down and stop. Even nudging it would not get it to restart.
They're cheap to buy on Amazon for around $28, so I have one on order.
Still need to trace out why the compressor does not run for zone 3 but I have a feeling it is the relay for that zone.
I have a Trane ac installed in my home which is about 30 years old and still very efficent. Recently, when the compressor and fan quit running, it shutters. I noticed that the fan blade does not seem to rotate freely as it slowes down. I was thinking it should rotate a little longer. Before I go out and purchase a new fan motor, am I correct in thinking it is the fan motor causing the shutter when it shuts off. I have stood there and I haven't seen the motor shake, but if you stand back away from the unit, you will see the whole unit shutter just for a second or two. No other problems with the unit that I have noticed.
Yes, I'm cheap and relying on your help.Read More
I just installed Senville LETO Series Mini Split , 9000 BTU 110/120V, (SENL-09CD-16).
It works fine on the Cool Mode, but when I turned to Heat Mode, there was nothing. The outside condenser stopped running.
I turned up the temperature to max (89 F) and it was still nothing. Switched to Cool and it was working.
I appreciate any help from the expert. Thank you in advance.Read More