Mini-Split Wiring Question
#1
Mini-Split Wiring Question
I want to add a mini-split heat pump to my detached garage workshop this year. I have several questions, but for now I will confine it to the most immediate need; power supply wiring.
My workshop is 24' x 24'x10' high ceiling. The HVAC contractor I spoke to recommended a 240V, 24,000 BTU mini-split. In looking at several of these units they show they use 10 amps.
I will need to add a new circuit for this. The distance from the circuit breaker to the AC disconnect will be approximately 100'. Would I need to run 20A or 30A service? And what size wire would I use?
My workshop is 24' x 24'x10' high ceiling. The HVAC contractor I spoke to recommended a 240V, 24,000 BTU mini-split. In looking at several of these units they show they use 10 amps.
I will need to add a new circuit for this. The distance from the circuit breaker to the AC disconnect will be approximately 100'. Would I need to run 20A or 30A service? And what size wire would I use?
#2
Connect the A/C to an existing panel in the building or run a new separate line ?
By code you are only allowed one circuit to a detached building.
That means you would run a larger cable and then use a sub panel in the building.
What do you have currently for power in the building ?
A 20A circuit using 12/2 w/g cable would be ok.
By code you are only allowed one circuit to a detached building.
That means you would run a larger cable and then use a sub panel in the building.
What do you have currently for power in the building ?
A 20A circuit using 12/2 w/g cable would be ok.
#3
I have a 100 amp sub-panel in the new, detached garage. 12/2 w/g is what I ran for all my outlets on a 20A circuit. I guess since the mini-split is running 240V I expected something different.
OK. 12/2 w/g. Got it. Thanks.
OK. 12/2 w/g. Got it. Thanks.