My unit outside is turning on and then 10 seconds later shuts off. The thermostat is a Honeywell RTHL 3550 model and is not clicking on like it used to. Not sure whether it's the outside unit or the thermostat. Please advise.
Thanks Fritoguy15

 

Top Answer

 
09-30-23, 06:25 AM
fritoguy15
fritoguy15 is offline
Member
Thread Starter
Join Date: Feb 2002
Location: Central Florida
Posts: 177
Upvotes: 0
Received 2 Upvotes on 1 Post
The drain line was clogged so the tech cleaned it out and we got our air back to normal. Thanks for all your help.
fritoguy15. 😎😎
 
  #2  
Old 09-28-23, 02:28 PM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
Have you checked to see if the primary condensate line is clogged-up and a float switch is turning the system off? After the system is off a while condensate water drains through the clog so the system is able to run again for a while again until the condensate water backs up again and the float switch shuts it down once again and it just keeps repeating over and over.


 
  #3  
Old 09-28-23, 02:31 PM
F
Member
Thread Starter
Join Date: Feb 2002
Location: Central Florida
Posts: 177
Upvotes: 0
Received 2 Upvotes on 1 Post
the outside drain line is dripping fine.
 
  #4  
Old 09-28-23, 02:35 PM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
Is the outside drain that is dripping a primary drain or a secondary (emergency) drain?

 
  #5  
Old 09-28-23, 02:39 PM
F
Member
Thread Starter
Join Date: Feb 2002
Location: Central Florida
Posts: 177
Upvotes: 0
Received 2 Upvotes on 1 Post
primary drain, no secondary drain line.
 
  #6  
Old 09-28-23, 05:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,883
Received 3,750 Upvotes on 3,362 Posts
I believe that is a battery operated thermostat.
That means there would be a cooling(Y) relay, a heating(W) relay and a blower(G) relay.
Relays not operating correctly usually indicate weak batteries.

If it's not a battery/thermostat problem then you will need a meter to check the 24vac line to the outside condenser. The problem your describing sounds very much like your are low on refrigerant and the condenser is cycling from the low pressure switch.

Please read first for A/C repair
 
  #7  
Old 09-29-23, 06:32 AM
F
Member
Thread Starter
Join Date: Feb 2002
Location: Central Florida
Posts: 177
Upvotes: 0
Received 2 Upvotes on 1 Post
The thermostat also has a R wire, and does have batteries in it. Plus the other wires you mentioned. I was wrong about the drain line it is a secondary line. Tech is coming later today to test for whatever is going on. Thanks.
Fritoguy15
 
  #8  
Old 09-29-23, 06:50 AM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
primary drain, no secondary drain line.
I was wrong about the drain line it is a secondary line.
If your secondary condensate drain line is dripping that definitely indicates the primary condensate line is blocked-up with a clog. The secondary condensate line should never have water coming out of it - even one drip.

Try to figure out where the primary condensate drain line is clogged-up. It may be clogged near the evaporator coil, or further down the line where is actually drains out. It may drain out to a bathroom lavatory just about the sink's p-trap, which is how most are installed to drain in newer construction. Regardless, the primary condensate drain line is clogged-up somewhere and needs to be cleared.






 
  #9  
Old 09-30-23, 06:25 AM
F
Member
Thread Starter
Join Date: Feb 2002
Location: Central Florida
Posts: 177
Upvotes: 0
Received 2 Upvotes on 1 Post
The drain line was clogged so the tech cleaned it out and we got our air back to normal. Thanks for all your help.
fritoguy15. 😎😎
 
CircuitBreaker, Kooter voted this post useful.
  #10  
Old 09-30-23, 07:23 AM
Kooter's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jan 2003
Posts: 861
Received 88 Upvotes on 81 Posts
Thanks for letting us know...
 
CircuitBreaker voted this post useful.
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: