Old home, 3 inch dryer vent, fire hazard?

My friend just bought an old house, it has a 3 inch dryer vent that disappears into a wall and exits at the roof. We bought a 4 to 3 inch conversion and hooked up his dryer. We went on the roof and air comes out freely, is it a fire hazard?
 
Sponsored Links
  #2  
Old 03-08-10, 04:04 PM
pugsl's Avatar
Forum Topic Moderator
Join Date: Mar 2008
Location: United States
Posts: 8,594
Received 29 Votes on 27 Posts
What kind of tubing is in the wall. If it is the old plastic flexible stuff replaced it.
 
  #3  
Old 03-08-10, 04:13 PM
Member
Thread Starter
Join Date: Mar 2010
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
it is metal going up through the roof like a smoke stack with no cover on it
 
  #4  
Old 03-08-10, 04:43 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 3 Votes on 3 Posts
You mean the 3" pipe sticks straight up to the sky? No cover? Buy a stack cover.
 
  #5  
Old 03-08-10, 04:50 PM
Member
Join Date: Oct 2006
Location: Wilmington
Posts: 4,219
Received 0 Votes on 0 Posts
If it is rigid steel duct, it may not be a fire hazard, but could violate local code. I personally would not want a dryer duct buried in the wall, but appears OK under IRC code. Rigid ducts is min .016" metal wall, no screws at joints. And it should be thoroughly cleaned periodically.

2006 IRC M1502.3 requires duct size per manufacturers recommendations, for most that is 4".
M1502.4-"transition ducts shall not be concealed within construction".... a transition duct is the flex duct from the dryer to the rigid duct. Max allowed is 8', no plastic allowed.
M1502.6-max duct length is 25', Each 45deg =2.5', each 90 deg=5'.
 
  #6  
Old 03-08-10, 05:28 PM
Member
Thread Starter
Join Date: Mar 2010
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
Originally Posted by Just Bill View Post
If it is rigid steel duct, it may not be a fire hazard, but could violate local code. I personally would not want a dryer duct buried in the wall, but appears OK under IRC code. Rigid ducts is min .016" metal wall, no screws at joints. And it should be thoroughly cleaned periodically.

2006 IRC M1502.3 requires duct size per manufacturers recommendations, for most that is 4".
M1502.4-"transition ducts shall not be concealed within construction".... a transition duct is the flex duct from the dryer to the rigid duct. Max allowed is 8', no plastic allowed.
M1502.6-max duct length is 25', Each 45deg =2.5', each 90 deg=5'.
wow.. great answers, thanks a lot! I am going to love this forum
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: