OK code says I must have some firestop installed. I plan on building the walls with 2*4 about 1" from the cinder block. How do I go about doing the firestop?
#2
If your worried about fire in the one inch space behind the wall. Just put a piece of 5/8 drywall on top of your top plate before you put it up, cut it 4-1/2" if yor using 2x4 framing, so it extends back the 1" to the block wall. Then use fire rated caulk to seal it to the block.