Power Head Not working


  #1  
Old 10-28-04, 06:56 PM
keithbas
Visiting Guest
Posts: n/a
Power Head Not working

I have a 3 zone baseboard heating system. 2 of my zone valves have stopped working. If I remove the power head while still wired the curculator kicks in. If I leave the head attached and manually open the valve I hear the value open but the circulator kick in. What is going on?
 
  #2  
Old 10-29-04, 08:47 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sounds like a Taco valve. If you take the head off with power applied, you most likely runied the valve. Possibly not if it is a gold head, but you probably should replace the heads. You may not have a large enough transformer but it only takes 40va for all 3 valves. Make sure the heat anticipators on the thermostats are set at .9 and if they don't open, replace them.

Ken
 
 