Multiple Brand Zone Valve wiring


  #1  
Old 11-27-04, 04:19 PM
karnfamily
Visiting Guest
Posts: n/a
Cool Multiple Brand Zone Valve wiring

Sorry about the possibly foolish question, but I am new to HVAC, but have a lot of experience with gen. plumbing and electrical work.
I have a 3-zone house. Currently I have 2 taco valves and one Honeywell valve all wired together. The problem is that the circulator is running continuously and I want to make sure that they are all wired together correctly. How should these all be wired? I can only find diagrams for wiring together the same type of valves.
Thanks
Dan
 
  #2  
Old 11-28-04, 05:54 AM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
Mixing brands makes a tedious job even worse. The end switch on the Honeywell triggers the circulator. If yours has screw terminals, I think it is terminal 3 & 4. If you take the cover off of the valve, you can see the end switch and where the wires go. On the Taco valves, terminals 2 & 3 go to the end switch. One of the switches must be triggered or the valve is open.

Ken
 
 