aquastat


  #1  
Old 11-29-04, 03:11 PM
leoc
Visiting Guest
Posts: n/a
aquastat

HI
I would like to know if there's a difference with a cold start aquastat or one that has the temp controls on it. I was told by my service tech that a cold start aquastat maintains 180deg only when there is a call for heat otherwise the boiler will not fire up. The reason why i ask is because i just got a peerless boiler installed and it came with this cold start aquastat, but after it was installed there was problems with it, so he put another aquastat on it the one with the high and low temp settings, he also told me the low temp setting on the aquastat was not being used just the high. So if i understand this right the water temp will always be 180deg? is this ok


thanks a lot
 
  #2  
Old 11-29-04, 06:57 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is a difference between the two controls. It is just as you described. The cold start one does not maintain any temperature in the boiler and only starts the burner when there is a call for heat. It will still stop the burner at the high limit. The other one maintains whatever temperature the low limit is set at until a call for heat and then it goes for the high limit. Maybe your tech clipped the wire for the low limit. The cold start control costs less so it would have been cheaper to use that control.

Ken
 
  #3  
Old 11-30-04, 03:13 PM
leoc
Visiting Guest
Posts: n/a
Thanks Ken,
I have one more question can i shut the boiler off in the summer?
Thanks again for the help.
P.S. Iam sure I'll post again.
 
  #4  
Old 11-30-04, 03:17 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
You can shut it off in the summer, but if you have a domestic coil in the boiler or a blank coil plate, you may have problems with the gasket. Give it a try.

Ken
 
  #5  
Old 11-30-04, 04:12 PM
leoc
Visiting Guest
Posts: n/a
Ken the boiler is without coil (peerless WBV-04 with a beckett) Iam not sure if i have a blank coil plate how can i find out
thanks
 
  #6  
Old 12-01-04, 05:12 AM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
Look around on the boiler. It is a steel plate with several bolts in it. Usually the jacket is cut out around it. A true cold start boiler should not have any gasketed surfaces in my opinion. They are the weakness.