oil furnace question

I have an american standard arcoliner furnace that is oil fired,seam heat. Does anyone know what the pressure regulator should be set at? It currently is set at 2.5 lbs.for cut in and at 1 lb on the differential.The system is rated for 15 lbs steam but the pressure only goes to about 3 llbs when the unit is running.Any way to get more pressure out of this unit? Thanks,Steve
 
Sponsored Links
  #2  
Old 01-18-05, 05:24 AM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Received 0 Votes on 0 Posts
More pressure = less heat. You would be better off to reduce the setting to not exceed 2 psi. It is very unusual to need more than 2 psi to heat a house. Excessive pressure (3+ psi) will hold the radiator vents closed and do other nasty things. You may have other problems.

Ken
 
  #3  
Old 01-19-05, 03:21 PM
stevie
Visiting Guest
Posts: n/a
oil furnace pressure

Ken,lowered the pressure,ran it for 24 hours to check it out,and as you prescribed the heat is great!Also using less fuel than before. Thanks! Steve
 